    One more issue. Suppose the transformer size is worked out. If the size of the OCPD for the transformer protection is smaller than the panels incomer circuit breakers (already provided), it could cause coordination problem.

  2. #22
    Join Date
    Nov 2007
    Posts
    779
    Quote Originally Posted by Sahib View Post
    One more issue. Suppose the transformer size is worked out. If the size of the OCPD for the transformer protection is smaller than the panels incomer circuit breakers (already provided), it could cause coordination problem.
    Not gonna happen. The usual thing is to work from the bottom up.

  3. #23
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Sahib View Post
    Sorry I do not know how Iam violating NEC......
    That is correct, you do not know so the best thing you can do for the OP is to shut up and observe.

  4. #24
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,914
    Quote Originally Posted by Sahib View Post
    One more issue. Suppose the transformer size is worked out. If the size of the OCPD for the transformer protection is smaller than the panels incomer circuit breakers (already provided), it could cause coordination problem.
    Inconvenience is more likely the proper thing to call it. Unless these "trailers" are serving as a public safety command center or a 911 call center or something similar where keeping the power on is critical.