    Cable-RHH

    http://www.southwire.com/ProductCata...odcatsheetOEM7

    so RHH and RHW-2 is the same wire?

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,838
    The sequel is never as good as the original except for The Godfather.
    If Billy Idol or John Denver is on your play list go and reevaluate your life.

  3. #3
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    4,876
    Quote Originally Posted by mstrlucky74 View Post
    For some reason I can't download that information. I suspect it just means that the Southwire product is multiple-listed. Why spend the money to list three separate products if one product will meet all the requirements, especially if there is almost no cost delta in production?

  4. #4
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    935
    Only that RHW-2 is 90*C in wet conditions versus its predecessor RHW which is 75*C rated.
    Guess they didn't want to call it RHHW instead.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,950
    Does RHH have a 2 hour fire rating for fire pumps?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    12,421
    Quote Originally Posted by infinity View Post
    Does RHH have a 2 hour fire rating for fire pumps?
    If I am reading this article correct: No.

    http://ecmweb.com/safety/safety-and-...cable-products

    Used to be apparently.

    "Type RHH/RHW cable that was formerly listed for fire resistance is no longer fire resistance listed by UL."
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,950
    Quote Originally Posted by jumper View Post
    If I am reading this article correct: No.

    http://ecmweb.com/safety/safety-and-...cable-products

    Used to be apparently.

    "Type RHH/RHW cable that was formerly listed for fire resistance is no longer fire resistance listed by UL."
    Yes that article is almost 4 years old, I believe the UL has restored the use of RHH with a 2 hour rating.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,706
    Quote Originally Posted by infinity View Post
    Yes that article is almost 4 years old, I believe the UL has restored the use of RHH with a 2 hour rating.
    I believe it's only 2 hour rated horizontal and not vertical(lost its listing)...need conduit to be run in vertical 2 hour rated enclosure( closet, shaft etc.)

  9. #9
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    12,421
    Quote Originally Posted by infinity View Post
    Yes that article is almost 4 years old, I believe the UL has restored the use of RHH with a 2 hour rating.
    Ooops. A bit dated, eh?

    If I get bored I will look again.
    "Electricity is really just organized lightning." George Carlin


    Derek