    Cable-RHH

    http://www.southwire.com/ProductCata...odcatsheetOEM7

    so RHH and RHW-2 is the same wire?

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    7,781
    The sequel is never as good as the original except for The Godfather.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  3. #3
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    3,685
    Quote Originally Posted by mstrlucky74 View Post
    For some reason I can't download that information. I suspect it just means that the Southwire product is multiple-listed. Why spend the money to list three separate products if one product will meet all the requirements, especially if there is almost no cost delta in production?

  4. #4
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    795
    Only that RHW-2 is 90*C in wet conditions versus its predecessor RHW which is 75*C rated.
    Guess they didn't want to call it RHHW instead.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    22,493
    Does RHH have a 2 hour fire rating for fire pumps?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    11,056
    Quote Originally Posted by infinity View Post
    Does RHH have a 2 hour fire rating for fire pumps?
    If I am reading this article correct: No.

    http://ecmweb.com/safety/safety-and-...cable-products

    Used to be apparently.

    "Type RHH/RHW cable that was formerly listed for fire resistance is no longer fire resistance listed by UL."
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    22,493
    Quote Originally Posted by jumper View Post
    If I am reading this article correct: No.

    http://ecmweb.com/safety/safety-and-...cable-products

    Used to be apparently.

    "Type RHH/RHW cable that was formerly listed for fire resistance is no longer fire resistance listed by UL."
    Yes that article is almost 4 years old, I believe the UL has restored the use of RHH with a 2 hour rating.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,230
    Quote Originally Posted by infinity View Post
    Yes that article is almost 4 years old, I believe the UL has restored the use of RHH with a 2 hour rating.
    I believe it's only 2 hour rated horizontal and not vertical(lost its listing)...need conduit to be run in vertical 2 hour rated enclosure( closet, shaft etc.)

  9. #9
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    11,056
    Quote Originally Posted by infinity View Post
    Yes that article is almost 4 years old, I believe the UL has restored the use of RHH with a 2 hour rating.
    Ooops. A bit dated, eh?

    If I get bored I will look again.
    "Electricity is really just organized lightning." George Carlin


    Derek

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •