Thread: Need clarification on 514.11 (Circuit Disconnects for Fuel Dispensing Facilites)

  1. #1
    Join Date
    Dec 2007
    Location
    California
    Posts
    578

    Need clarification on 514.11 (Circuit Disconnects for Fuel Dispensing Facilites)

    Article 514.11(A) states:

    514.11 Circuit Disconnects.
    (A) General.
    Each circuit leading to or through dispensing
    equipment, including equipment for remote pumping systems,
    shall be provided with a clearly identified and readily
    accessible switch or other acceptable means, located remote
    from the dispensing devices, to disconnect simultaneously
    from the source of supply, all conductors of the circuits,
    including the grounded conductor, if any.
    Single-pole breakers utilizing handle ties shall not be
    permitted.
    Use of the terms "switch" (singular) and "disconnect simultaneously" it appears that it must be one switch that disconnects all power. So what if there are more than two circuits that need to be disconnected. The enclosed emergency stop switches I've found can accommodate no more than two stacked DPST switches. Since both the hot & neutral legs must be broken, that's one DPST switch per circuit, thus a maximum of two circuits.

    A second question I have is regarding the circuits that are affected by 514.11(A). Our fleet dispenser requires two circuits (one 230VAC circuit for pump motors and one 115VAC circuit for electronic controls, solenoids, & dispenser internal lighting). Outside the dispenser, we are installing hose reels with power rewind (115VAC). Would these hose reels be considered on a "circuit leading to or through dispensing equipment"?

  2. #2
    Join Date
    Jan 2017
    Location
    North Dakota USA
    Posts
    61
    I'll take a stab at it.

    So the way I understand it is, when the code says "disconnect simultaneously" it is referring both the ungrounded and grounded (hot&neutral) conductors of each circuit. It would basically be a switched neutral breaker for a 120v circuit, and a two pole breaker for a 240v circuit.

    The way I normally use emergency stop button are in conjunction with a shunt trip breaker which powers the entire fueling panel. If the entire panel can not be powered down in the case of an emergency, then one case use the e-stop in conjunction with contactors for the circuits within that classified area. Should be a NC contact for contactors and NO for the shunt option if I'm thinking correctly.

    In regards to the second question, the way I understand it is they all need to be shut down. Hose reel, disp lighting, pump motor, etc. this can be done with one of the above methods. I myself like using shunt panels. No problematic contactors in the future.

  3. #3
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    The few I have worked on used a six pole switch as the means to disconnect all circuits to each pump individually.

  4. #4
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,348
    Quote Originally Posted by Jon456 View Post
    Article 514.11(A) states:



    Use of the terms "switch" (singular) and "disconnect simultaneously" it appears that it must be one switch that disconnects all power. So what if there are more than two circuits that need to be disconnected. The enclosed emergency stop switches I've found can accommodate no more than two stacked DPST switches. Since both the hot & neutral legs must be broken, that's one DPST switch per circuit, thus a maximum of two circuits.

    A second question I have is regarding the circuits that are affected by 514.11(A). Our fleet dispenser requires two circuits (one 230VAC circuit for pump motors and one 115VAC circuit for electronic controls, solenoids, & dispenser internal lighting). Outside the dispenser, we are installing hose reels with power rewind (115VAC). Would these hose reels be considered on a "circuit leading to or through dispensing equipment"?
    Remember that that you must meet the requirements of both 514.11 and 514.13. This can get complicated if you have more than just power circuits involved such as a card reader, audio, etc. In most cases today, the only way to accomplish this and be compliant is to use a listed product that is made for this purpose. All the petroleum equipment makers have stuff available that is made for this purpose.
    The old school methods of shunt trip breakers, contactors, etc cannot be used for a variety of reasons.

  5. #5
    Join Date
    Jan 2008
    Posts
    147
    Sq D makes a switch where you can add contacts to do power, and then 2 wire loop for pump data, card reader and intercom. Cat 5 which is becoming really common in pumps and more so in the future for EMV card readers is a problem.
    http://www.schneider-electric.us/en/...er-disconnect/

    Power Integrity makes a box that handles Pump loops, card readers, intercom and Cat 5 .
    http://www.powerintegritycorp.com/in...age-disconnect.

    I generally use NO relays for all 120v loads to switch hot and neutral, Estop holding relays closed until pushed. Sometimes I use 3 pole contactor and switch sub panel. Making sure fire suppression and other items that need to stay on are not in that panel

    Not sure how one can use a shunt trip as that leaves neutrals still connected unless all your loads are 208-240v?

  6. #6
    Join Date
    Jan 2017
    Location
    North Dakota USA
    Posts
    61
    Yes. Our petroleum people always supply the low voltage equipment for credit card/pump control. They usually have little disconnect switches inside them to turn off each disp individually.

    As as for the shunt trip integration, can one not use a 3 phase shunt breaker and use one pole for disconnecting the neutral and the other two for the line voltage phases?

  7. #7
    Join Date
    Jan 2008
    Posts
    147
    Wouldn't a 3 phase shunt trip have ungrounded conductors on all 3 poles? I don't know if they make a 4 pole, 3 hots and 1 grounded in a shunt trip but I doubt it. I know they make 3 pole, 2 hots and switched neutral but it isn't a shunt trip.

  8. #8
    Join Date
    Jan 2017
    Location
    North Dakota USA
    Posts
    61
    Quote Originally Posted by wallyworld View Post
    Wouldn't a 3 phase shunt trip have ungrounded conductors on all 3 poles? I don't know if they make a 4 pole, 3 hots and 1 grounded in a shunt trip but I doubt it. I know they make 3 pole, 2 hots and switched neutral but it isn't a shunt trip.
    I would imagine someone makes a 4 pole shunt breaker, but probably ridiculously expensive. We normally have single phase 240v submersible or gravity fed pumps. Where we do have 3 phase submersibles, they are powered through a Mag VFC by FE Petro, normally, and if you interrupt the dispenser hook signal, there will not be any power present out there. So basically the e-stop is going to shut down the panel powering the dispensers, and therefore there will be no disp hook power. If you just need to do maintenance on the submersible, one can just use the breaker for power interruption.

  9. #9
    Join Date
    Dec 2007
    Location
    California
    Posts
    578
    Just to be clear, "to or through dispensing equipment" does not include lighting or CCTV mounted on the canopy above the dispenser (above the classified area), correct?

  10. #10
    Join Date
    Dec 2007
    Location
    California
    Posts
    578
    I think the best way to solve this problem is with a shunt-trip breaker upstream of the sub-panel that feeds the dispenser. But that means the shunt-trip breaker must disconnect two hots and the neutral. Is there a special switched-neutral, 2-pole shunt-trip breaker? Or do I simply use a three-pole, lug-style shunt-trip breaker and use one of the poles for the neutral?