Results 1 to 9 of 9
Thread: Why is this Lutron dimmer so pricey?
  1. #1
    Arcing Lutron 3-way dimmer switch, one of 4 in a conference room, need to replace it, $162.00 from a local wholesaler, anybody paying less? Ridiculous IMO.
    Attached Images Attached Images
    Mt. Falls, Va.
    "Not a sermon, just a thought"
    A licensed electrically-related individual
  2. #2
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    4,622
    I looked up the part number, that price seems about right. Also looked up 120V dimmers, they are quite a bit cheaper, so no doubt 277V is a smaller production run/more expensive. $162 isnt bad, one place listed the same at $60 more. Fluorescent compatible is probably the other biggy, aside from being a 1000W (1500W?) dimmer.
  3. #3
    Join Date
    Apr 2008
    SW Florida
    Posts
    545
  4. #4
    Join Date
    Mar 2003
    New England
    Posts
    13,190
    Try ebay.
    Fluorescent dimming? How has that not been relegated to the trash heap yet?
  5. #5
    Join Date
    Jun 2010
    Posts
    1,928
    Nova T(star) is architectural grade. Look up Nova T for any load type and the list price is quite high.
  6. #6
    Quote Originally Posted by peter d View Post
    Try ebay.
    In this case, no. This Lutron system has been in the building since 2005. Unless the dimmers/ballasts are discontinued, and no longer available, we will be maintaining them. The ballasts are around $100. The auditoriums in both of my buildings have Lithonia dimming systems, breaker panels have built-in manual control panels, and aux. computer controlled controls.
    Mt. Falls, Va.
  7. #7
    Join Date
    Jun 2010
    Posts
    1,928
    Quote Originally Posted by JFletcher View Post
    That's a Lutron 3-wire system.
    Dimmer electronics doesn't handle the load and it's functionally similar to 0-10v and has a slight advantage but it is proprietary and 0-10v has taken the majority share. You have two hots. One is connected directly to power through a switch, the other one is dimmed like a normal dimmer and served to each ballast but it is only watched as dimming reference.
    The slight advantage is that phase angle communication isn't affected by voltage drop like 0-10v and is more resistant to interference. Dimming doesn't affect harmonics or power factor much and do not cause buzzing or RFI because each ballast receives full line voltage and dimmer doesn't manipulate power handling line.
  8. #8
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,830
    Sounds like that dimming ballast would be pretty pricey too in that case!
  9. #9
    Join Date
    Feb 2017
    Atlanta
    Posts
    2
    Hi Mtfallsmikey,
    Yes, that is a bummer, but the Lutron dimmer is actually worth the price. It has loads of really great features such as auto-load sensing capability, green LEDs to indicate light level, 10-year power - failure memory, acoustically quiet operation, voltage regulation, color consistency, universal dimmer, and many more.