  1. #21
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,719
    Quote Originally Posted by Holop View Post
    I believe ground screw needs to be listed for such means. Example I've seen retrofit can light is supplied with a zinc green color tek screw included with the kit. It's kinda catch 22 because inspectors themselves don't know about this and almost always require documents for the screw or retro can light.


    Sent from my iPhone using Tapatalk
    General rule is in 250.8.

    Screw must engage no less then two threads or have a nut on the back side. The typical "ground screw uses 32 threads per inch, so with no nut on the back side that means it must be threaded into at least 1/16" of metal to attain two threads engaged.

    Connections that are a part of a listed assembly are permitted even if they break the other rules here, the listing covers them.

    Only place NEC requires a green colored screw is for main bonding jumpers that are screw type jumper (the bonding screw for panelboards and disconnects for the most part).

  2. #22
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,534
    I see this post is a month old and probably already resolved, but since I noticed the date after I typed out all the following...

    Quote Originally Posted by GoldDigger View Post
    Note that you cannot use a nut instead of two threads with a self-tapping screw.

    mobile
    Self tapping screws would cross-thread in a nut made for a machine screw.

    OP, if the fixtures were old enough to be replaced in the first place, then they very well be on the verge of needing new ballasts anyway, even if the 277V ones work on 120V. It's not like 4 bulb 120 - 277V ballasts are expensive anyway:

    https://www.1000bulbs.com/product/63...1MYaArhq8P8HAQ
    Electricians do it until it Hertz!

  3. #23
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,464
    Quote Originally Posted by Holop View Post
    I believe ground screw needs to be listed for such means
    No, screws used for grounding or bonding do not need to be listed and do not need to be green. Look at most mechanical lugs used for this purpose, they are normally attached with run of the mill screws, bolts, and nuts.

    Roger
    Moderator

  4. #24
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,464
    Quote Originally Posted by kwired View Post
    General rule is in 250.8.



    Only place NEC requires a green colored screw is for main bonding jumpers
    You might want to look at 406.10

    Roger
    Moderator

  5. #25
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,719
    Quote Originally Posted by roger View Post
    You might want to look at 406.10

    Roger
    Right, but that screw is already installed for you, unlike the panelboard bond screw that if you lose it, you may be tempted to use whatever fits.

  6. #26
    Join Date
    Feb 2003
    Location
    Tennessee
    Posts
    1,650
    Quote Originally Posted by kwired View Post
    Right, but that screw is already installed for you, unlike the panelboard bond screw that if you lose it, you may be tempted to use whatever fits.

    Its hard to believe you can't use a self tapping screw but you can use that little green slide clip.

    Ronald : 0

  7. #27
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,719
    Quote Originally Posted by ronaldrc View Post
    Its hard to believe you can't use a self tapping screw but you can use that little green slide clip.

    Ronald : 0
    Those clips look cheesy, but most don't let go all that easily if you are trying to remove them. Too little amount of thread engagement leads to poor connection, the spring clip at least does maintain pressure to make good contact.