    Coil testing

    I have a Siemens Coil 120volt for 100amp lighting contractor. It requires momentary power to open and close contacts. Coil has two sets off poles that I assume would be moving the magnet in two different directions, but I have O resistance on one set off poles and correct resistance on the other set. Does one assume there is a short in the coil?
    Attached Images Attached Images  

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,079
    If you are measuring the coil contacts directly then you apparently have one coil with an open winding, thus defective
    If you are measuring thru contacts, it may just be the normal holding contact open.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    16,680
    Does "O resistance" in your post mean zero resistance (a short) or Overload resistance, an open circuit?

  4. #4
    Join Date
    Jan 2012
    Location
    United States
    Posts
    12

    short

    Quote Originally Posted by GoldDigger View Post
    Does "O resistance" in your post mean zero resistance (a short) or Overload resistance, an open circuit?
    0 meaning short.
    Im assuming, i don't have any diagram or info for the coil, that,referring to the pic, the poles you see are two sets of coil connections within the contactor.

  5. #5
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,250
    0 as meaning the two probes of the ohm meter are touching each other directly (shorted), or 0 as you hold the two leads into the air touching nothing (open)?
    Tom
    TBLO

  6. #6
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,250
    A shorted coil would typically show a blown fuse or control circuit damage somewhere. An open coil would show lack of operation.
    Tom
    TBLO

  7. #7
    Join Date
    Jan 2012
    Location
    United States
    Posts
    12
    Quote Originally Posted by ptonsparky View Post
    A shorted coil would typically show a blown fuse or control circuit damage somewhere. An open coil would show lack of operation.
    The control circuit is momentary contact 120volt to close and open, three position on/on/off switch. The contractor is closed and will not open when 120volts is applied. No issues with control.

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,364
    Quote Originally Posted by pfactor2 View Post
    The control circuit is momentary contact 120volt to close and open, three position on/on/off switch. The contractor is closed and will not open when 120volts is applied. No issues with control.
    If you have zero resistance, I'd say the coil is shorted. It should draw high current when you try to energize it, unless it already did that at some point and took out some component in the control circuit.

  9. #9
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,079
    Unless things have changed there are two things you might check before you install a new coil:
    1. Be sure the armature moves freely. If it does not seat correctly the coil will burn out.
    2. If its like the mechanically held contactors I've worked on in the past, the control circuit to the coil often goes thru a set of auxiliary contacts that opens and removes coil voltage once the contactor is set. make sure the contacts are working properly.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  10. #10
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    14,514
    hard to tell without more information. coils are generally low resistance and can be close to zero ohms when measured with a common voltmeter.

    best bet is to test it on your bench and see if it works by applying the appropriate voltage to the coil(s).

    if it works great, if it does not work throw it away and buy a new one.

    it is just basically a giant latch relay.
    Bob