Page 1 of 3 123 LastLast
Results 1 to 10 of 25
Thread: Erratic LED Lighting
  1. #1
    Join Date
    Mar 2017
    SW Florida
    Posts
    14
    I recently purchased an old Florida house that was in dire need of lighting (among other things). After replacing the 200A, 20 space panel with a 200A, 42 space panel I started doing electrical upgrades in the house. Thinking I'd save some electrical bill $$$ going with LEDs, I bought some LED can lights and dimmers that the lighting distributor approved as compatible. I settled on 3" and 4" cans with trims rated at 9 watts each.
    For the kitchen and lanai lighting I ran a single 15A circuit fed by 14/2 NC cable. On that circuit are:
    • (6) 3" cans controlled by (1) Lutron Maestro MACL-153M and (1) Lutron Maestro MA-R (kitchen ceiling)
    • (4) 3" cans controlled by (1) Lutron Maestro MACL-153M and (1) Lutron Maestro MA-R (soffit)
    • (3) 3" cans controlled by (1) Lutron Maestro MACL-153M and (1) Lutron Maestro MA-R (island)
    • (6) 4" cans controlled by (1) Lutron Maestro MACL-153M (lanai)
    • (2) 3" cans controlled by (1) Lutron Maestro MACL-153M (above sink)
    • (2) 4" cans controlled by (1) Lutron Maestro MACL-153M (above bar)
    When the lights in the lanai are on and I turn on the kitchen ceiling lights, the lanai lights brighten then dim back to where they were.
    When the lanai lights are turned off (regardless of the state of other lights on the circuit) 5 of the 6 lights remain lit but very dim so you can only see it when it's dark. The only one that is completely out is the one first fed from the dimmer and through which the remainder are fed.
    I did the installation a little at a time (I don't move so fast anymore) and the lanai & bar were the last sets of lights I installed. Everything seemed to work fine up to adding the bar & lanai lights.
    Any thoughts on why the LEDs are acting up?
    Thanks,
    Jim
    IBEW (retired)
  2. #2
    Join Date
    Jun 2010
    Posts
    1,928
    Quote Originally Posted by Jim M426 View Post
    You thought wrong. Lighting energy consumption is not a significant percentage of residential energy profile and making LED conversions(not upgrade) with high expectations means feeding quarters into a vending machine that dispenses the same quantity of nickels. Changing from 20 space to 42 space don't really resonate with saving power usage either. LED lights are usually the most expensive option as they have the most problems, require the most time and effort to commission properly when combined with dimming. How far are you up to just in parts expense for all that Lutron gear? I'd bet it takes many years if ever for savings from power savings from those lights to even pay off the cost for all that.
    You've given us the details about the controls, but what about the specific details of the load? Compatible doesn't mean absolute freedom from noticeable annoying behaviors.
    Phase cut LED dimming is touchy and susceptible to problems for technical reasons. It is the type you're using, and it is the most common type in residential applications. When you turn on the kitchen light, it draws an inrush current which causes a very brief voltage dip. The L. E. D. ballasts in your lanai lights are tripping out. Does it only happen when the lanai lights are deeply dimmed?
    Microprocessor dimmers have a bleed current and the particular design of LED ballast that happens to be used in your fixtures/lamps allows the tiny amount of current flowing through the fixtures to impose current on the LEDs. You only need a couple microamps to make an LED give off visible light. If you throw a regular incandescent lamp into the string, I bet they'd extinguish.
    Thanks,
    Jim
    IBEW (retired)
    You're using a combination of modern fads that makes the system prone to shakes and rattles like you're experiencing that is expensive to commission as the final fine tuning requires hand fitting by trial and error.
  3. #3
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,723
    I disagree on the savings from LED lighting. I heat, cook, dry and heat water with Nat Gas so my electrical loads are minimal. In my basement I had square recessed cans, they were 100W, I went to 26 W CFL and now have 13 W LED, 5 each that's a considerable savings.
    I have no problems with my LEDs, they are far better than the CFLs. I have not had a screw in A base LED fail over 3-4 years, in the same time I had many CFLs fail.
    Moderator-Washington State
    Ancora Imparo
  4. #4
    Join Date
    Mar 2003
    Washington
    Posts
    10
    LED residential lighting
    I would also agree that there can be substantial savings when installing LED lights. I have replaced 15 of the 65W floods in my house with replacement LED floods. I have also swapped out another 12-15 or so incandescent bulbs with the LED equivalent bulbs inside and outside. Over the last 3 years I have not had to replace a single one. Got most from Costco or other big box store on sale or with manufacturers rebates. Even my wife has noticed a reduction in our electric bill. Looks like a 10-20% savings so far. No CFL's in my house any more!! Even went to the 4 foot LED fixtures in my shop.
  5. #5
    Join Date
    Jun 2010
    Posts
    1,928
    Because, LEDs are very labor intensive to commission
    Quote Originally Posted by tom baker View Post
    Savings depends on annual hours. I've found vacancy sensors great for limiting the duration lights can be accidentally left on. It works as a normal manual on/off switch. Count down starts from the last motion detected, which can be set from about a minute to 30 minutes. Many have auto-restart if movement is detected within 30 to 60 seconds of shut off before reverting to manual on mode. It's much less burdensome than twist timer since count down resets whenever there's motion.
    That is compared to CFLs, which do not dim well except for externally ballasted 4-pin type.
    Bunch of expensive dimmers he bought suggests he's quite demanding on aesthetic performance.
    It requires 1% dimming to "seem like 10%" because of non-linear response of human vision and that's the expectation held by common people. Flicker free, full range, stable, silk smooth fade to dark is very technically challenging to do with LEDs especially with phase cut dimming and presents an enormous burden.
    Dimming to 10% lumen output feels like 32% as bright and this draws quite a few complaints about LED lamps with comments such as "it only seems to dim to about a 1/3 and it says 10%....". Going below 10% ("feels like 1/3") have negligible energy advantage while making it exponentially increasing commissioning difficulties, stability issues and other performance problems for technical reasons.
    Hand fitting to make ever fluid products work correctly and getting it stabilized requires time, which must be added to the bill, thus making it an very expensive technology to implement.
    Getting LEDs to work flawlessly, consistently and reliably over the entire range is usually EXTREMELY difficult. Usually, the trouble is on the lower end setting.
    If you dim to the lowest level it will remain on, it may not come back on if shut off at this level and turned back on without bumping it up a significant level, then bringing it back down. Whether done manually or automatically, this will cause a pronounced flash.
    Dimmable LED ballasts are far more prone to flipping out at line noise than incandescent. For example, other loads switched (as threadstarter complained). I know that the ballast in some CREE bulb gets confused when a fan is switched off on the same circuit and causes the lamp to completely shut off and restart even when it is not on a dimmer.
    Some combination have a sore band. When you're inside the sore band, the lamp exhibits shimmer.
    So I still conclude that getting LEDs to satisfy high end decorative dimming comes at a very high cost that it blows away any savings.
    Finally, flicker, color and brightness unevenness becomes more pronounced under deep dimming and presently, LEDs exhibit very unnatural looking color as they're dimmed. Color remains pretty much the same but turns bluer on the extreme low end,which is the opposite of incandescent lamps which leads to "just don't like the color" dissatisfaction.
    Residential grade LED lamps have "years of life" assuming 3 hrs per day. 65W saving (100w bulbs on dimmer, likely not used at full level all the time, so if dimmed power use is 75W and L. E. D. substitute uses 10W) at 3 hrs per day is an annual saving of 71 kWh, which is <$10 per year per lamp saved.
    Even if added cost for the fixture is small, the increased cost in using high cost specialized controls and added labor cost for commissioning with time consuming adjustments and likely multiple visits may make it impossible to save anything. This thread is a very example of very common LED commissioning frustrations.
  6. #6
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,363
    Thanks,
    Jim
    IBEW (retired)
    any chance you have a loose neutral somewhere
    in the mix? it's a long shot, but....
    those dimmers are particularly tolerant, but sometimes stuff
    just has teething problems... i'd try this....
    take one of those dimmer out of the mix, and substitute
    a lutron diva c-l, and see how it works. DVCL-153P
    if it doesn't work with that, you've got lights that aren't
    ever gonna dim well, imho.
    i've got above 50 DMF led can lights in my house, i'm
    running those dimmers, and while you can dim them
    almost to black, they won't fire at that low level with those
    dimmers, but really nothing that isn't 0-10v. controls will.
    and yeah, you can save some money on your electric bill.
    if i turn on every led in my house, and dim them all the
    way down, they draw total, about 40 watts, measured with
    a fluke 345.
    and electric-light has some strong opinions about LED lighting
    in general... but you probably already got that.
    let us know how it turns out.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  7. #7
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Fulthrotl View Post
    I had the same thoughts with one circuit effecting another.
  8. #8
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,609
    Quote Originally Posted by iwire View Post
    OP says all the lights are on the same circuit.
    So, I doubt it's a problem with the neutral.
    What happens when you 'back up time' and disconnect the bar and lanai lights? Does the problem go away?
    Cheers and Stay Safe,
    Marky the Sparky
  9. #9
    Join Date
    Mar 2017
    SW Florida
    Posts
    14
    Thanks for the replies. I've had many of the same thoughts about possible problems. The wiring is good, I've checked it several times to see if there was any installation problems I missed. Everything tells me it boils down to the dimmers and LEDs.
    So everything works fine until I install the lights in the lanai and at the bar. Both the latter are 4" trims, as opposed to all 3" trims previously installed. Something quirky in manufacturing the 4" trims? I don't know. I know little about troubleshooting LED lighting because I never ran into it on the job.
    The other difference is the lanai and bar are each single pole switched. Could the companion dimmers on the 3-ways be working to stabilize the current? That would be something I'd have to take to Lutron but I wouldn't expect any eureka response.
    In my last house I turned to the Maestro dimmers because I wanted dimming control at all locations and became hooked. All the lights there were incandescent. I had over (70) 6" cans with 65W lamps in that house and my electric bill showed it. After installing the LEDs here, I've barely noticed the bill increase. But I was skeptical about dimming LEDs to the low level I like in the evening. The Maestro dimmers allow me to program the dimmers to get to that level. All looked good until I added the last lights.
    Disconnecting the bar and lanai lights, and no problems. But the problems have all been in the lanai lights. Those are the ones that, when dimmed, brighten up when adjusting dimming for the kitchen ceiling lights. They are the only switched sets that have 6 lights on them. But the lanai lights (all 4") is the only set that never turns fully off. The dimmer has a tab on the bottom of it that is supposed to completely cut the power to the fixtures, designed for changing out a lamp. When I pull the tab out, the lanai lights remain in the same dimmed state. So there is still a trickle current there. That tab is designed to completely open the circuit, cutting the trickle completely. That's not happening.
    I'm going to have measure the current at each fixture through all states of dimming and once the tab is pulled and see what comes up. I think the dimmers are affecting one another through the trickle current. I don't think there's a bleed over through the wiring but that tab issue has me wondering.
    One other thing that is probably completely unrelated is all the switch boxes are tied together by plastic flex. Then I pulled the travellers and whatever wires I needed through the flex. Feeds to the lights are done in 14/2 NM. I come from the land of conduit where NM is sacrilege but I can't see how the NM drops to the switch box could be causing any cross wire bleed over. It's probably just my conduit conditioning causing me to feel guilty for using NM.
    I've got a couple of other thoughts I have to check out and see how that goes. Thanks again for the responses. My enthusiasm to solve this has been rejuvenated.
  10. #10
    Join Date
    Mar 2008
    Posts
    9,609
    Suspecting a bad dimmer, I would check for voltage across the load terminals after the tab was pulled out. If present, which I think will be the case, the next thing I would do would be to disconnect the hot load connection and see what happens. If the lights go out, check for voltage at the hot load terminal. If voltage is present and you KNOW the line and load hots are wired correctly, I would replace (or swap) the dimmer and re-check.
    Marky the Sparky