Results 1 to 5 of 5
Thread: grounding and bonding
  1. #1
    Join Date
    Mar 2017
    california
    Posts
    1
    greetings forum,
    I was recently in a class and a test question was posed as such. "bonding plays a far more important role in protecting people from shock than grounding." The astute teacher said the answer was true. I contended, unsuccessfully, that one is not effective without the other. There must be something I am not understanding as I still believe an effective bonded system must also be grounded(i.e. grounding electrode). Help me understand. Thank you
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,033
    The teacher is correct. Even though a system may be grounded (earthed) it plays very little if no part of personnel safety at voltage levels below 1000V. Bonding the systems parts with a low impedance path back to the source is what opens OCPD's
    Roger
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,079
    Quote Originally Posted by sparklet569 View Post
    greetings forum,
    A totally ungrounded circuit can be perfectly safe, since no point on that circuit can source current to ground as a result of a single fault. Bonding of mental that is not connected to any circuit point will not make a difference except when two faults are present at the same time. In that case bonding is a second level safety precaution, and it does not hurt to ground the bonded mesh.
    If you have a grounded circuit, on the other hand, with one conductor of the supply tied (bonded) to ground, then everything that is not normally energized should be bonded AND tied to ground to prevent a hazardous voltage from appearing as the result of a fault.
  4. #4
    Join Date
    Jul 2005
    Tennessee
    Posts
    15,765
    A swimming pool is a good example. To assure than any surface with which one has contact is at the same potential, all conductive elements of the pool, including the water, are bonded together. The bond is present even if no components are intentionally grounded. Stray voltages from power transmission elements can be present and pose a hazard unless proper bonding is assured.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  5. #5
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,120
    Quote Originally Posted by GoldDigger View Post
    Yes, Many people see the word "ground" or other forms of the word and think "safety" or "safer". I like to say that system grounding is just a system topology and not about safety. Both have advantages and disadvantages.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
Posting Permissions
  • You may not post replies
  • You may not edit your posts