Thread: WAREHOUSE EMERGENCY/EGRESS LIGHTING

  1. #1
    Join Date
    Apr 2006
    Location
    Upstate S.C.
    Posts
    821

    WAREHOUSE EMERGENCY/EGRESS LIGHTING

    Working on a 250' x 250' warehouse/production facility. 150' x 240' is 18' high rack storage, 100' x 150' production area, 50' x 90' office, and 50' x 90' misc. Lighting is LED at ~20' AFF. Production and misc. areas are dimmable. The office is mostly dimmable. At the moment the office lights are 120V and the rest is 277V, but the office can be 277V if needed. There is a single 277V lighting panelboard.

    I can't in good conscience put in battery packs because of the battery maintenance issues. But going to an emergency generator requires lots of dedicated conduits which are costly and potentially dedicated fixtures. But, even with that it should (?) be the least long term cost. And with dimmable fixtures, it will be interesting how (if) to use any of them for the egress lighting.

    What is the "preferred" method(s) to providing emergency lighting for large areas?

    Thanks,
    RC
    It's my name going on that drawing, not yours. If what you want ain't right, it ain't going on the drawings!

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,484
    What battery maintenance issues? You test them annually and do what needs done. Why is this any harder than any needed maintenence all the other lights in the facility? Why is having a generator a better option? It's not like they are maintenance free. Far, far from it as a matter of fact.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  3. #3
    Join Date
    Apr 2006
    Location
    Upstate S.C.
    Posts
    821
    ANYBODY WITH COMMENTS, ETC.??
    It's my name going on that drawing, not yours. If what you want ain't right, it ain't going on the drawings!

  4. #4
    Join Date
    Dec 2010
    Posts
    1,272
    Quote Originally Posted by Ragin Cajun View Post
    ANYBODY WITH COMMENTS, ETC.??
    Posting in caps is bad.
    The more they overthink the plumbing, the easier it is to stop up the drain

  5. #5
    Join Date
    Dec 2010
    Posts
    1,272
    You can use a BCELTS on dimmable fixtures. You might want to consider a central battery inverter instead of a generator.
    The more they overthink the plumbing, the easier it is to stop up the drain

  6. #6
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    4,186
    Quote Originally Posted by Ragin Cajun View Post
    ANYBODY WITH COMMENTS, ETC.??
    ActionDave already replied. Anyway, most hotels and warehouses here have something like these:

    http://www.e-conolight.com/standard-...z-AaAmaO8P8HAQ

    or something similar x 20, 30, 200, etc, and they far exceed 40,000ft2. Get an extension pole to test them monthly, replace the whole fixture every 6-8 years or so. The battery and lights will last that long. I dont know of a cheaper method.

    Battery back ups to troffer lights are harder to test and the batteries cost 5-10x what separate egress lighting costs. I'd use integrated EXIT signs/elights where possible
    Electricians do it until it Hertz!

  7. #7
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Ragin Cajun View Post
    ANYBODY WITH COMMENTS, ETC.??
    OK,

    I hate typical EBUs, they are ugly and not that great lighting areas up. I would much prefer a generator feeding the regular lighting.


    However, if you have no real need for backup power other than the egress lighting a generator is going to be the most costly way to go. There are the ongoing costs of required upkeep, oil changes, exercising etc.

    The up front costs for an emergency genset ATS and seperate wiring clearly much higher.

    You can buy a new EBU for little more than the cost of a replacement battery for it.

  8. #8
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,368
    Inspected a ton of warehouse over the last decades. 95% are done as JFletcher notes above.\
    Apparently the most cost effective as most were wired by the low bidder
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,924
    Have forklift operator turn on the headlights on the forklift during a power outage

  10. #10
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    3,788
    What specific fixture ? Most can be ordered with a battery backup factory installed. Your other option would be remote inverters at ground level that are more easily accessible.