Page 2 of 2 FirstFirst 12
Results 11 to 14 of 14
Thread: class 1 division 2
  1. #11
    Join Date
    Mar 2017
    fayetteville ar.
    Posts
    5
    yes it is
    its a class one div 2
  2. #12
    Join Date
    Mar 2017
    fayetteville ar.
    Posts
    5
    question
    this application is for an inspection booth in a paint room area. it has ventilation , etc . its a monarail conveyor line and im hanging an led light 120v and using a lb75 aluminum boby for connection to light fixture
  3. #13
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    4,935
    • Aluminum RMC and its associated fittings are fine where installed per Sections 344.10(A)(3) and (B)(2).
    • They must be listed per Section 344.6 but NOT specifically for Classified Locations.
    • Section 501.10(A)(1)(a) and by back reference in Section 501.10(B)(1)(1) specifically permit various forms of RMC and their associated fittings in Classified Locations.
    • Class I, Division 1 boxes and fittings must comply with Section 501.10(A)(3).
    • Class I, Division 2 boxes and fittings only need to comply with Section 501.10(B)(4) with a few limitations as noted previously.
    • Section 500.8(C)(6)(a) does not require boxes and fittings to be specifically marked for Classified Locations.
    Your Aluminum LB is fine in the application as described.
    That should cover the OP.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
  4. #14
    Join Date
    Mar 2017
    fayetteville ar.
    Posts
    5
    Quote Originally Posted by rbalex View Post
    thank you
Posting Permissions
  • You may not post replies
  • You may not edit your posts