Page 1 of 2 12 LastLast
Results 1 to 10 of 18
Thread: Definition Of Conductors
  1. #1
    Join Date
    Apr 2003
    Michigan
    Posts
    21
    Good Afternoon Everyone,
    I am having a friendly debate with an electrical counterpart regarding what the conductors on the attached are defined as. What we have is a 1/4" x 4" continuous copper bar around the perimeter of the substation room and from that copper bar we have 4/0 conductors to the associated substations. I am trying to keep my question as vague as I can, so as not to influence anyone's answer.
    Your assistance is appreciated.
    Thank you.
    Attached Images Attached Images
  2. #2
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,770
    Quote Originally Posted by tnt8197 View Post
    Thank you.
    I don't understand the question. Is this a feeder vs. branch circuit thing question?
    Cheers and Stay Safe,
    Marky the Sparky
  3. #3
    Join Date
    Apr 2003
    Michigan
    Posts
    21
    My apologies, the copper bar around the substation room is a ground bar and this is the main point the system. Hope this clarifies.
    Thank you
  4. #4
    Join Date
    Apr 2003
    Michigan
    Posts
    21
    Here is the full drawing of the area. I was trying not to show this so as not to influence anyone's answers.
    Thank you again.
  5. #5
    Join Date
    Mar 2008
    Posts
    9,770
    Thank you
    I will go with EGC.
    Marky the Sparky
  6. #6
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Bonding Conductor or Jumper. A reliable conductor to
    ensure the required electrical conductivity between metal
    parts required to be electrically connected.
  7. #7
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,868
    I would call them grounding electrode conductor's
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  8. #8
    Join Date
    Sep 2016
    Longmont, CO
    Posts
    177
    Thank you.
    I'm not sure what the official term would be if there is one, but I consider it a supplemental EGC. (off subject a bit, I've been on this rant for awhile) The gas and oil industry seems to like supplemental grounding, including ground rings in the earth, connected to every metallic object in a plant including a metallic MCC/PDC building. I understand the importance of grounding and bonding, but in a building with switch-gear, etc. already grounded per NEC, this supplemental grounding system adds a parallel path for fault currents which doesn't follow the supply conductors, which seems to me to be a negative. The NEC has been altered over the years for instance to make sure this doesn't happen on SDSs, etc. Thoughts? If this should be a new thread, I understand.
  9. #9
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,381
    Quote Originally Posted by Jim1959 View Post
    I've done a lot of work on cell sites and they have a similar earthing scheme, along with everything, and I mean every single cotton picking thing, metal having a copper bonding jumper above and beyond the normal EGC back to a big copper buss. I don't see any problem with it.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  10. #10
    Join Date
    Apr 2003
    Michigan
    Posts
    21
    Quote Originally Posted by iwire View Post
    Why would you consider this a bonding jumper in lieu of a grounding conductor? The conductors are going from the main grounding bus bar to the downstream portion of the unit substations? Wouldn't that be the main grounding conductor for the separately derived system?
Posting Permissions
  • You may not post replies
  • You may not edit your posts