250.32 (A) says that a structure supplied by either a feeder or branch circuit shall have a grounding electrode or grounding electrode system installed. However, 250.32 (A) exception states that a structure supplied by a single branch circuit doesn't need a grounding electrode. Even if a structure is only supplied by a single branch circuit, this single branch circuit could still supply a huge amount of power to a structure. Why would this structure disconnect not require a grounding electrode?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I can only assume that the thinking is that the equipment grounding conductor will handle the situation. In past codes the equipment grounding conductor was not allowed to double as a grounding electrode conductor but with the 2014 it appears that in many cases the equipment grounding conductor can be used as a grounding electrode conductor. Not sure this answers ours question.... best I could come up with
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
250.32 (A) says that a structure supplied by either a feeder or branch circuit shall have a grounding electrode or grounding electrode system installed. However, 250.32 (A) exception states that a structure supplied by a single branch circuit doesn't need a grounding electrode. Even if a structure is only supplied by a single branch circuit, this single branch circuit could still supply a huge amount of power to a structure. Why would this structure disconnect not require a grounding electrode?

What do you mean "huge amount of power"?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The ground electrode will not make a significant difference in the fault current impedance, do I would be more inclined to question why the building ground is required in the first place given a properly sized EGC.
I guess that lightning induced currents would be bypassed around a high EGC impedance at high frequencies. Which brings us right back to why it would not be needed if only a branch was run to the building. :)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
... In past codes the equipment grounding conductor was not allowed to double as a grounding electrode conductor but with the 2014 it appears that in many cases the equipment grounding conductor can be used as a grounding electrode conductor. ...
In my opinion the only code that has ever prohibited using a single conductor as both the EGC and the GEC was the 2011 code. The 2014 exception to 250.121 puts us back exactly where we were before 250.121 was added to the code in 2011.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
as for a huge amount of power - suppose one had a 200HP motor as the only load under a 3 sided shed.

it is a structure, but it only has one branch circuit so no GE is required.
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
as for a huge amount of power - suppose one had a 200HP motor as the only load under a 3 sided shed.

it is a structure, but it only has one branch circuit so no GE is required.

I know, I just wanted clarification. Not that a GE would make a difference if it was 200 amps or 20 amps.
 