    Quote Originally Posted by Carultch View Post
    Do you know any examples of equipment with ring KO's that are listed for 277V or 277/480V bonding? I'd like to see how this is noted on a datasheet. I understand that these will be a lot more heavy duty than ordinary knockouts, and more difficult to remove.
    There was a thread a while ago where someone posted a reference to the KO's in disconnect switches not be tested as suitable for grounding over 250 volts. Most 1900 and 4 11/16 boxes that I've seen are so listed.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #12
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,001
    Quote Originally Posted by infinity View Post
    There was a thread a while ago where someone posted a reference to the KO's in disconnect switches not be tested as suitable for grounding over 250 volts. Most 1900 and 4 11/16 boxes that I've seen are so listed.
    Datasheet link please.

  3. #13
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    22,507
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #14
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,089
    If you look at Pg A-14 it notes boxes that are approved for 600v application without bonding jumpers.
    http://www.hubbell-rtb.com/literatur...ccessories.pdf
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  5. #15
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,001
    Quote Originally Posted by augie47 View Post
    If you look at Pg A-14 it notes boxes that are approved for 600v application without bonding jumpers.
    http://www.hubbell-rtb.com/literatur...ccessories.pdf
    Thanks Augie. I knew these existed in concept, but I wasn't really sure how I would find one in a product search, or know how to confirm it on the product markings.