Page 18 of 21 FirstFirst ... 81617181920 ... LastLast
Results 171 to 180 of 209
Thread: Why do they both trip???
  1. #171
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Ingenieur View Post
    http://www.talcofire.com/Glossary.html
    Booster/Jockey Pump:
    An auxiliary pump used to maintain system pressure without starting the main pump. These pumps are not designed to keep up with full system demand, their only function is system pressure maintenance
    Right booster pump, jockey pump, pressure maintenance pump likely other names as well but not 'fire alarm booster panel'.
  2. #172
    Join Date
    Jan 2011
    United States
    Posts
    7,136
    Quote Originally Posted by iwire View Post
    Go back to bed.
    I'm not finished haunting this forum for the day yet
    I'm in over my head...
  3. #173
    Join Date
    Jul 2015
    NJ
    Posts
    98
    OK so I read most of this thread. We have the exact situation for one of our clients. The breaker will trip when going from generator back to utility. It will be a series coordinated fault, tripping breakers straight down the line (3) 225A breakers. There's a transformer at the end at 75kva. We adjusted the instantaneous setting and the problem went away. We felt the problem was due to asymmetrical fault inrush current because it would depend on where in the sine wave it was switched over. This site is also customer owned including transformers upstream.
  4. #174
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,668
    Quote Originally Posted by 310 BLAZE IT View Post
    There is no fault, just a temporary spike in current when that transition is made.
  5. #175
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,668
    VFD's wont start a motor already spinning unless they have "on the fly starting" abilities and is enabled, for similar reasons.
  6. #176
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by mbrooke View Post
  7. #177
    Join Date
    Jan 2016
    PA
    Posts
    5,057
    booster pumps have a fire alarm control panel with pressure controls, starter, alarming, etc.
    hence 'fire alarm booster panel'
    I do not see 'fire alarm booster panel' on your pnl schedules, only 'fire alarm control panel' and 'fa power suply'
    regardless
    imo the breakers are set too low and are of the wrong type, no toc element (is that even code compliant for this application?)
    perhaps fire alarm, elevator and emergency ltg may be exempt if desired from oc protection? (only need sc)
    swap them out for I/t and your problems will disappear and you will have better protection (I think you can leave the main, just crank it up to 800%/1600 A)
    The difference between genius and stupidity is that genius has its limits.
  8. #178
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,836
    Apparently you have not bothered to look up the actual breaker data sheets yourself.
    Magnetic trip only breakers are relatively rare. Magnetic only mounted into standard panelboard construction are extremely rare, and may no longer even exist.
    Just because you can, doesn't mean you should.
  9. #179
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,474
    regardless
    If you use that term in conversation with anyone who is familiar with both fire alarm and sprinkler, I'm betting 99 out of a hundred will assume you mean a notification appliance booster power supply. especially since it says "alarm", and the hundredth will ask you to repeat the question.
  10. #180
    Join Date
    Mar 2003
    New England
    Posts
    13,224
    We call them "NAC panels" here.