    Does anyone have information on how to calculate the secondary line voltages for this type of transformer? Information generally would be gratefully received!!!
  2. #2
    Join Date
    Jul 2006
    Posts
    7,567
    Quote Originally Posted by RogerRoger25 View Post
    How about an explanation of how you are using this and why you need to know? Because if it's just the 6 phases you want to know about, that's easier to describe than the 9 possible connections available.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  3. #3
    Join Date
    Sep 2008
    UK
    Posts
    11,061
    Got a diagram?
  4. #4
    Join Date
    Sep 2008
    UK
    Posts
    11,061
    Quote Originally Posted by Jraef View Post
    Do you think he means hexaphase?
  5. #5
    Join Date
    Jan 2016
    PA
    Posts
    5,075
    6 phase
    ph-ph voltage = ph-neut/gnd voltage
    The difference between genius and stupidity is that genius has its limits.
  6. #6
    Join Date
    Sep 2008
    UK
    Posts
    11,061
    Quote Originally Posted by Ingenieur View Post
    6 phase
    Got a diagram of a forked star?
  7. #7
    Join Date
    Feb 2008
    Texas
    Posts
    880
  8. #8
    Join Date
    Jul 2006
    Posts
    7,567
    That lower diagram is something I was aware existed in theory, but have never needed to implement. 6 phase (hexaphase) as shown in the upper diagram on that page, used as an input to a 12 pulse rectifier, yes. But the "forked wye" thing is not necessary for that. Still, there are people who sit around thinking about this sort of stuff for all kinds of off beat uses.
  9. #9
    Join Date
    Jan 2016
    PA
    Posts
    5,075
    Is this xfmr used to do something similar?
    D - DDD
    4160-1400/1400/1400 0 deg/+20 deg/-20 deg
    3500 kva labeled scr application
    ties a 4160 bus to a large vfd that powers a 4160 3500 hp motor
    only used for starting then a contactor transfers in
    http://forums.mikeholt.com/showthread.php?t=182722
  10. #10
    Join Date
    Sep 2008
    UK
    Posts
    11,061
    Hexaphase is commonly used for six-pulse rectifiers for high current low voltage rectifiers. There is one device (SCR typically) in each leg. The merit is that you have just one semiconductor voltage drop as opposed to two with a full wave rectifier. The devices are subjected to a higher PIV but if the system is just a few tens of volts that is not usually a critical factor.