    Grounding a concrete tank

    I have a problem, we have been asked to come up with a grounding scheme for a concrete tank. Normally no problem, slap a few ground rods and cadd weld to the rebar. Our civil guys have spec-ed out the rebar as epoxy coated and that is my problem, attaching to the rebar won't work. Anyone else encounter a situation like this and how did you get around it?

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    7,770
    If it were a swimming pool you would make your own bonding grid out of 8AWG copper. Same principle should work for your tank.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  3. #3
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    14,514
    have them add some uncoated rebar just for you to connect to.

    why are you "grounding" a concrete tank? and what are you "grounding" it to are important questions to answer first though.
    Bob