Page 1 of 2 12 LastLast
Results 1 to 10 of 13
Thread: 230.79(C) - one-family dwellings
  1. #1
    Join Date
    Feb 2014
    Charlotte, NC
    Posts
    336
    So I read this as all single family dwellings require a minimum 100A service disconnecting means.
    What about individual units within a two or multi family dwelling? Typically I provide minimum 100A regardless of the diversified load but I have another engineer who is trying to make the OCPDs for apartment units 80A.
  2. #2
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,032
    I think you are in the wrong section. What you are describing is not the service but a feeder and is based on the calculated load. You should be looking in 220
    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.
  3. #3
    Join Date
    Feb 2014
    Charlotte, NC
    Posts
    336
    Quote Originally Posted by luckylerado View Post
    So you answered my follow up question... I agree with your response that it is not a service, I just typically provide 100A because my loads tend to be close to that anyway with the type of units I design around.'
    Another question is in regards to section 225.39(C), which states, "For a one family dwelling, the feeder disconnecting means shall have a rating not less than 100A, 3-wire"
    I know that 225 is for "outside branch circuits and feeders" but then why would you include such a broad statement?
  4. #4
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,032
    Quote Originally Posted by lielec11 View Post
    Got me.. IS this a single family dwelling? Each of the separate units are not considered single family dwellings unless they stand alone.
  5. #5
    Join Date
    Feb 2014
    Charlotte, NC
    Posts
    336
    It is just a general question that came up from a friendly discussion. For the sake of your question let's just say it is part of a multifamily building. If fed from a common meter center then the unit load centers can be whatever size the calculations in 220 dictate, correct?
    Edit: I just looked up the code definition of "dwellin unit" and "dwelling, single family" .... I think I was mistakenly lumping these into the same category.
  6. #6
    Join Date
    Mar 2014
    Utopia
    Posts
    1,366
    Agreed...you were lumping the two together. The application as expressed lead to the following:
    225.39(D) All Others. For all other installations, the feeder or branch-circuit disconnecting means shall have a rating of not less than 60 amperes.
    Assuming the engineer provides the calculated load calculation in accordance with Art.220 the disconnection means aspect of your question is answered again in 225.39 (D).
    Comments based on the 2017 National Electrical Code.
    *All code responses are based on the 2017 National Electrical Code[NEC]
  7. #7
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,016
    Let's be clear, if this is a multifamily building then, IMO, the feeder does not have to be 100 amps to each apartment. 225.39 is for single family dwelling.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,288
    225 is also for outside feeders. If you are supplying a stand alone single family dwelling that 100 amp disconnect capacity applies.
    If you are feeding a dwelling unit within a building you only need to supply it with whatever art 220 load calculation applies to the dwelling. A very basic dwelling will have at least 2 - 1500 VA small appliance branch circuits plus 3 VA per square foot. If you get all that into 400 square feet you may only have a load calculation of only 4200 VA, and could supply it with a 35 amp 120 volt feeder or a 20 amp 120/240 feeder.
  9. #9
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,016
    The op was mentioning perhaps multi-family dwelling. I don't see the nec states what size must be run to the units.
  10. #10
    Join Date
    Feb 2014
    Charlotte, NC
    Posts
    336
    Quote Originally Posted by kwired View Post
    You just described every new apartment unit in NYC, Brooklyn, etc., etc...
    Quote Originally Posted by Dennis Alwon View Post
    I don't think it does, this was the basis for my original post to see if any of you code guru's on here knew of a certain section I haven't come across yet...