    System grounding for dettached bldg

    Hi ,
    the 400A residential service is located at the corner of the property, stand alone, dettached;

    if I install a 400A distribution panel with main on the exterior wall of the house, do I need to system-ground it
    as well as the main 400A stand alone service????
    two sys. grounding in one property?????


    THANK YOU

  2. #2
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    20,484
    400A service disconnecting means (ref: stand-alone, corner of property) is where the Main Bonding Jumper is installed.

    At the 400A MDP on house exterior is where you connect the building grounding electrode system to the EGC. Maintain EGC and grounded [neutral] separation at the MDP.
    I'll never get there. No matter where I go, I'm always here.

  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    2,945
    Quote Originally Posted by Toros View Post
    Hi ,
    the 400A residential service is located at the corner of the property, stand alone, dettached;

    if I install a 400A distribution panel with main on the exterior wall of the house, do I need to system-ground it
    as well as the main 400A stand alone service????
    two sys. grounding in one property?????


    THANK YOU
    Is there a service disconnect at the corner or just a meter? Generally speaking, every structure served needs a disconnect and a grounding electrode system so yes you could have multiple GES on a property.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #4
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by electrofelon View Post
    Is there a service disconnect at the corner or just a meter? Generally speaking, every structure served needs a disconnect and a grounding electrode system so yes you could have multiple GES on a property.
    Thanks, I was going to bring that up.

    It seems the need for a grounding electrode system at a simple service pedestal varies by area. Some will say that the pedestal is not 'served' because it does not use electricity. I disagree with that but I also see it as a reasonable interpretation.

    IMO the NEC has required GES at a pedestal, things may have changed with the new definition of structure. I have not really put any thought into it yet.

  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    2,945
    Quote Originally Posted by iwire View Post
    Thanks, I was going to bring that up.

    It seems the need for a grounding electrode system at a simple service pedestal varies by area. Some will say that the pedestal is not 'served' because it does not use electricity. I disagree with that but I also see it as a reasonable interpretation.

    IMO the NEC has required GES at a pedestal, things may have changed with the new definition of structure. I have not really put any thought into it yet.
    Yeah, I would have to look over the wording again to offer a more thorough opinion. Also, I have seen POCOS requires a GES at a pedestal with no disconnect.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"