Originally Posted by
Toros
Hi ,
the 400A residential service is located at the corner of the property, stand alone, dettached;
if I install a 400A distribution panel with main on the exterior wall of the house, do I need to system-ground it
as well as the main 400A stand alone service????
two sys. grounding in one property?????
THANK YOU
Is there a service disconnect at the corner or just a meter? Generally speaking, every structure served needs a disconnect and a grounding electrode system so yes you could have multiple GES on a property.
Ethan Brush - East West Electric. NY, WA. MA