SCCA versus AIC internal to utilization equipment (elevator)

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
A submittal from an elevator vendor included information about a circuit breaker that was internal to their control panel. It had an AIC rating of 5000 amps. Our calculation shows an available fault current at that location of 9000 amps. Does their breaker need to be replaced with one that has an AIC rating of 10kA or higher? My boss thinks so, and I don?t think it would be a bad idea. But is it required? The vendor is asking for a large increase in price to change out the breaker.

Looking at it from the vendor?s perspective, my take would be that the elevator equipment is UL listed as an entity, and the NEC therefore has no jurisdiction.

Looking at it from the perspective of ?what could go wrong,? the only fault that the breaker would see is one that is internal to the elevator equipment. If that fault were as high as 9000 amps, then their internal breaker might not be able to trip. Rather, it might have its contacts welded together, thus allowing the fault to continue unabated. The event would be terminated by the fused disconnect upstream of the elevator controller. In the meantime, the fault would destroy the controller, so why should we care that the breaker is also destroyed?

Comments? Opinions? Is this actually covered in the NEC?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I believe their Listing would require a single overall SCCR value. The values of the interior components are considered only by the listing agency.
They either need to supply a panel that meets the available fault current, or you need to 'insert impedance' in order to lower your available fault current. How are your specs written?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Generally control circuits do not require an SCCR.
But breakers have AIC ratings. We would not have noticed anything, except for the fact that the submittal had a description of a breaker that was internal to their equipment, including the 5kA rating of that breaker.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
But breakers have AIC ratings. We would not have noticed anything, except for the fact that the submittal had a description of a breaker that was internal to their equipment, including the 5kA rating of that breaker.

I am not sure it matters any. Only power circuits have SCCR.

There is no recognized means of evaluating anything other than power circuits.

However, if the control circuit is tapped from a power circuit without a xfmr, then there could be an issue.

Does the control panel as a whole have a SCCR?
 
Last edited: