    pvc conduit separation

    Are there any restrictions in the separation of pvc conduits inside the trenches, if ,for example, with ampcal software we calculate that we have enough separation with 3 inches between pipes?

  2. #2
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    869
    I've done several commerial jobs with trenches full of pvc pipes just stacked several layers deep (i.e. no spacing). They always passed inspection.

    Sent from my SCH-I535 using Tapatalk

  3. #3
    Join Date
    May 2011
    Posts
    3,695
    Quote Originally Posted by Coppersmith View Post
    I've done several commerial jobs with trenches full of pvc pipes just stacked several layers deep (i.e. no spacing). They always passed inspection.
    In my opinion you've gotten lucky. See 310.15(B)(3)(b).

  4. #4
    Join Date
    Jul 2003
    Location
    MA
    Posts
    2,007
    Quote Originally Posted by jaggedben View Post
    In my opinion you've gotten lucky. See 310.15(B)(3)(b).
    So, how much space would be required?
    0.001" is a space.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  5. #5
    Join Date
    May 2011
    Posts
    3,695
    Quote Originally Posted by tkb View Post
    So, how much space would be required?
    0.001" is a space.
    So get some 0.001 material and stick it in between.

    In all seriousness, my point was simply that I worked on a job where the inspector dinged us for stacking conduits on top of one another like Coppersmith described. So if it's never happened to you then you've just gotten lucky that the inspector doesn't know of that code section or chooses not to enforce it.

  6. #6
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    869
    Quote Originally Posted by jaggedben View Post
    In my opinion you've gotten lucky. See 310.15(B)(3)(b).
    All it says is "spacing between conduit, tubing, or raceways shall be maintained". I don't see where it says how much space.

    One of the jobs I did was for a roller coaster. One trench from the control building had 40 4" PVC conduits stacked 10 wide and 4 high. (Not my company's job. I was working for another contractor at the time.)

  7. #7
    Join Date
    May 2011
    Posts
    3,695
    Quote Originally Posted by Coppersmith View Post
    All it says is "spacing between conduit, tubing, or raceways shall be maintained". I don't see where it says how much space.
    ...
    Sure, but if they are stacked one right on top of the other then you don't have any spacing. I am neither defending it as a particularly sensible rule, nor am I saying that every inspector will raise this issue. I'm just saying you've been luckier than me if you done that many jobs and no one has ever brought it up, since the language is there in the code.

  8. #8
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,215
    Quote Originally Posted by jaggedben View Post
    Sure, but if they are stacked one right on top of the other then you don't have any spacing. I am neither defending it as a particularly sensible rule, nor am I saying that every inspector will raise this issue. I'm just saying you've been luckier than me if you done that many jobs and no one has ever brought it up, since the language is there in the code.
    Well in a sense, you still do, because it is physically impossible for any two objects to truly touch. But that's splitting hairs on what "touching" actually means.

    I think the intent of this rule, is so that no conduit in the trench is structurally loaded by another conduit. You maintain enough space that you can see with the naked eye between each conduit, and you are all set to meeting this rule. Either install plastic supports or backfill a layer of sand for the next layer vertically.

  9. #9
    Join Date
    May 2011
    Posts
    3,695
    Quote Originally Posted by Carultch View Post
    Well in a sense, you still do, because it is physically impossible for any two objects to truly touch. But that's splitting hairs on what "touching" actually means.

    I think the intent of this rule, is so that no conduit in the trench is structurally loaded by another conduit. You maintain enough space that you can see with the naked eye between each conduit, and you are all set to meeting this rule. Either install plastic supports or backfill a layer of sand for the next layer vertically.
    Given that the rule is in a section on adjusting for temperature, I assumed the intent is to prevent transmission of heat from one raceway to another, or build-up of heat if adjacent raceways are both heating. How this section exactly achieves preventing that is a bit beyond me though.

  10. #10
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,375
    When we have small ditches and a lot of conduits, we'll more often than not cut 12" pieces of 1/2" emt and drive them between the conduits every 10' to maintain separation. For duct banks, we typically use T&B chairs for spacing.