Hi,
Ill be installing my first 3 phase inverter, actually 2 of them. The inverter specs say 25 amps per phase of output continuous current. I planned on installing a 3 pole 100 amp breaker per inverter (25 amps per phase x 1.25) and sizing the conductors for 100 amp ampacity. Am I looking at this right? I feel like I am missing something (and should probably know this).
If I am looking at it right, I am confused in that the inverter termination points say #6 AWG max.
Thanks for your help!
Ill be installing my first 3 phase inverter, actually 2 of them. The inverter specs say 25 amps per phase of output continuous current. I planned on installing a 3 pole 100 amp breaker per inverter (25 amps per phase x 1.25) and sizing the conductors for 100 amp ampacity. Am I looking at this right? I feel like I am missing something (and should probably know this).
If I am looking at it right, I am confused in that the inverter termination points say #6 AWG max.
Thanks for your help!