    480V circuit in EMT

    I've been informed that a coworker of mine overheard someone say that you can't put 480V circuits in EMT conduit. I couldn't find any justification for this comment in Article 358 Electrical Metallic Tubing. Can someone please clarify?

  2. #2
    Join Date
    Mar 2003
    Location
    New England
    Posts
    12,905
    It's false.

    He might be talking about a job spec, but if so, it's a very unreasonable one.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    22,712
    You can put 480 in MC cable so why would EMT be prohibited?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    17,455
    Quote Originally Posted by Malteser View Post
    I've been informed that a coworker of mine overheard someone say that you can't put 480V circuits in EMT conduit. .........
    If that's true, I've installed miles of Code violations. I suspect you'll find it on page 37 of the Urban Legend Electrical Code.

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,922
    NM cable is rated for 600 volts. You may very rarely see it used on 277/480 volts, but it can be used as long as there is no restriction on NM for other reasons.

  6. #6
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    6,195
    I see that on a lot of industrial project specs, especially Water / Wastewater plants. But it's not a code thing, it's an engineer's preference thing.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  7. #7
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by kwired View Post
    NM cable is rated for 600 volts. You may very rarely see it used on 277/480 volts, but it can be used as long as there is no restriction on NM for other reasons.
    We used to run a lot of 480 & 277 in NM. That pretty much stopped when the NEC restricted NM above dropped ceilings.

    Don't snip that 12/3 going by thinking 'no big deal its 120 volt travelers', its really a 3 phase 480 circuit to a fan. POW!

  8. #8
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,064
    Quote Originally Posted by 480sparky View Post
    If that's true, I've installed miles of Code violations. I suspect you'll find it on page 37 of the Urban Legend Electrical Code.
    I'd like to see Mike Holt publish that book, explaining common NEC myths, how they came to be, and what the reality is on that subject matter.

  9. #9
    Join Date
    Mar 2003
    Location
    New England
    Posts
    12,905
    Quote Originally Posted by iwire View Post
    We used to run a lot of 480 & 277 in NM. That pretty much stopped when the NEC restricted NM above dropped ceilings.

    Don't snip that 12/3 going by thinking 'no big deal its 120 volt travelers', its really a 3 phase 480 circuit to a fan. POW!
    And 90% of the electricians hearing this died from heart attacks just pondering 480 volts on NM cable.

  10. #10
    Join Date
    Jan 2007
    Posts
    2,461
    Quote Originally Posted by iwire View Post
    We used to run a lot of 480 & 277 in NM. That pretty much stopped when the NEC restricted NM above dropped ceilings.

    Don't snip that 12/3 going by thinking 'no big deal its 120 volt travelers', its really a 3 phase 480 circuit to a fan. POW!
    More like KAAAABOOOOMMMM>.....