    CT Cabinet Raceways

    Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft

  2. #2
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,450
    Quote Originally Posted by Sparky3601 View Post
    Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft
    Yes, 230.43. You would have to pay attention to the extra bonding requirements though. Some POCOs may have an issue with this even though the NEC permits it.

  3. #3
    Join Date
    Mar 2017
    Location
    Windsor, CO
    Posts
    2
    Thank you for the reply. I knew 230.43 permits it, I wasn't sure if there was an "exposed to physical damage" article that I was overlooking