  1. #11
    Join Date
    Feb 2003
    Somewhere over the rainbow
    Posts
    3,279
    Attachment 17085
    "You will" not "will you"
    Edward
    The only thing I know, is the progressive discovery of my ignorance
  2. #12
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,524
    Quote Originally Posted by Sparky220 View Post
    Please elaborate on you're statement
    A regular breaker does not care if the the circuit to the fridge is completed through the neutral conductor, the equipment ground conductor, or both.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  3. #13
    Join Date
    Mar 2017
    Cloverdale,Va.
    Posts
    7
    Explain dangers.
    This is called objectionable current. It creates a parallel path for current to return to the source. Mike Holt has a video on this.
  4. #14
    Join Date
    Jun 2010
    Posts
    1,928
    Three pronged dryer receptacle which was allowed until NEC 1996 bonded the chassis to neutral and did not have a EGC to panel.
    Broken neutral is more common before the meter where it is exposed to the elements. When the neutral is lost, your washer has path to ground and the center tap neutral (depending on where the break is) through the EGC and possibly the water supply if it is connected with stainless braid wrapped hose and attaches to grounded water line. So you end up building 120v between dryer and washer cabinets. It was phased out because of this danger. The risk is much higher with a metal frame tool because the cord is handled much more frequently. Loose neutral in a power strip means the chassis becomes hot only when the tool is activated.
    If it is moved to an older house and the chassis is not connected to neutral, you'll have a floating frame. If moved to a newer house and the frame is bonded, you inadvertently create a neutral to ground bonding at the dryer.
  5. #15
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,716
    If another grounded object should contact whatever is connected to this bootlegged EGC, you have parallel path(s) for neutral current to flow over objects not intended to carry current.
    "stray voltage" problems are almost always a result of unintended current paths of the grounded conductor.
    This sort of bootleg may go without any noticeable problem for years in some cases. If in a wood framed building with no other grounded objects in the vicinity you can have full 120 volts on the frame of an appliance and never have a nearby ground reference to cause you to notice it. Of course if you have full 120 and bootlegged EGC, you probably have completely open neutral and the appliance doesn't operate, but my point here is there is no shock hazard in that situation because there is no grounded object within reach.
  6. #16
    Join Date
    Mar 2016
    The Motor City, Michigan USA
    Posts
    708
    (from Wiring Simplified)
  7. #17
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by kwired View Post
    Just want to say that "grounded object" does NOT have to be electrically grounded per classic or NEC definition. The aforementioned air compressor that bit me... July, sweating like crazy (why do all of these shock stories begin with that?) I grab the handle of the compressor to pull it, wheels are locked up. For more leverage, I place my other hand on a nearby jet-ski trailer...several hundred pounds of metal... those rubber wheels did not help me, I got smashed (shocked) hand-to-hand. The tongue of the trailer was on a wooden block. Had my body's resistance not been so low, I might not have even noticed it. As it was, it was very painful and about the most dangerous way to get shocked.
    The compressor had a fault in it. I pulled the 3 prong receptacle, only to find 2 wires connected. So the compressor frame sat at 120V to ground until it tried to find another path to the source, through me. That event was 20+ years ago, it was what got me interested in electrical; I didnt want that to happen again. The same day I learned about GFCI receptacles and installed one, and got a new compressor.
  8. #18
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,602
    Had an inspector tell me once, he would rather see the jumper from neutral to EG terminal at a device vs nothing. I didn't ask him why the heck do I spend so much time in Code classes if that is your thoughts. Carpenters that had done the remodel replaced old 2 wire with new devices and jumpered all of them.
    Tom
    TBLO
  9. #19
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by JFletcher View Post
    Please do not take this the wrong way I am sure you got the shock you said you did but I feel there had to be a path to ground beyond rubber tires and wood blocks.
    Was it all wet?
  10. #20
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,716
    Quote Originally Posted by iwire View Post
    Was it all wet?
    I agree. Modern (and for past 50 or more years) tires would likely have been conductive enough to help eliminate static charge buildup, but are not low enough resistance to pass any significant current at 120 volts.