    sers feeder cable ?

    can you run 4 wire sers feeder cable al in a commercial bldg. apts do any other I codes require this I cant find this anywhere in the nec

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    31,991
    It depends on how the building is typed. Is it type I, II, III, IV or V

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,265
    Also it cannot be use above drop ceilings in other than one or two family dwellings.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Aug 2008
    Location
    New England
    Posts
    1,469
    Quote Originally Posted by infinity View Post
    Also it cannot be use above drop ceilings in other than one or two family dwellings.
    That may be changing in NH. It already has in MA,VT, and ME
    "Appliances and wiring will burn out to protect fuses"