    Look for transformation from nominal 480V to nominal 600V.

    575V is a 'Canadian' utilization voltage, finding it on a motor nameplate is similar to finding 460V on a US motor.
    Just because you can, doesn't mean you should.

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,360
    Quote Originally Posted by Ingenieur View Post
    (480/575)^2 = 0.697 or ~70% or 7 kw
    ???

    it is rated at 575 / 10 kw
    P = v^2 / R
    take the ratios and R cancels (it is a constant)
    It is rated 575 / 10 kW.

    Bring it to me and most 480 volt nominal applications I am around typically run at an actual voltage of 495 to 500, but as Jim mentioned most motors connected to it will say 460 on their nameplate. A heater like OP has probably will say 480 volts on it's nameplate if intended to run on 480 volt nominal.

  3. #13
    Join Date
    Oct 2013
    Location
    newburgh,ny
    Posts
    362

    See this all the time

    Sell it as is! Do not try to get it working, $1000-1500 for transformer. If you try to convert it you will lose 1/3 output as said, plus you need a motor and control transformer and ANYTHING that is not know now.

    You see this all the time with someone who got a GREAT deal on something with the wrong voltage, wrong phase or frequancy.
    A cowboy may get thrown , but they always get up and walk forward.

  4. #14
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,360
    Quote Originally Posted by just the cowboy View Post
    Sell it as is! Do not try to get it working, $1000-1500 for transformer. If you try to convert it you will lose 1/3 output as said, plus you need a motor and control transformer and ANYTHING that is not know now.

    You see this all the time with someone who got a GREAT deal on something with the wrong voltage, wrong phase or frequancy.
    On this item yes, get rid of it is likely best option. Had a customer one time purchased a big dry ingredient mixer - food production grade, mostly all stainless, 25 HP drive motor, but the motor was 575 volt motor. It was a NEMA standard frame motor and was well worth buying a new 230/480 volt motor for it. I think the old motor eventually was sold with other scrap metal.