Thread: 20A recep on 15A circuit?

  1. #21
    Join Date
    Mar 2003
    Location
    New England
    Posts
    12,901
    Quote Originally Posted by user 100 View Post
    Not to pile it on here- but even if there was a full 20 amps on that ckt, the #14 would very likely safely handle that load indefinitely.

    Violation, sure (in most cases....). Imminent danger, no.

    The amperage tables were designed with a cushion in mind- which FTR, I see nothing wrong with.
    You beat me to it. #14 is not going to melt down or get damaged by 20 amps of load. In fact, the ampacity table used to list #14 as being suitable for 20 amps before it was revised.

  2. #22
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,370
    The way I see it: an appliance with a 5-20p (rare as they are) on it can draw 16A continuous or right at 20A non-continuous. Both of those numbers are higher than the allowable maximum ampacity of 14ga wire and/or a 15A breaker. Now, why there is the exception for a simplex 20A to be on a 15A individual branch circuit, I dunno, the same parameters are still in play, tho there is no chance of any other load on that circuit. I suppose the CMP decided that 16A continuous on a 15A breaker/#14 is ok in that instance, much the same as using #14 on a 20A breaker to a motor load is one of the few times you can exceed 15A on #14. Welders are the only other thing that comes to mind.

    In a nutshell, there are only a few exceptions to installing receptacles on circuits where the receptacle rating exceeds the OCPD's ampacity. 20A duplexes on a 15A circuit is not one of those exceptions. and tho JNOE's install is a code violation, in reality a HO will never ever find a 20A plug in appliance to use, and tossing spec/hospital grade receptacles for cheap ones is arguable a less safe install, but that's neither here nor there....

    These 'exceptional' installs are largely academic anyway because nearly every appliance that uses 15A/12A continuous will have mfg instructions to use a 20A circuit/#12 wire.
    Electricians do it until it Hertz!

  3. #23
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    3,911
    Quote Originally Posted by JFletcher View Post
    Isnt that the other way around? One single (simplex) 20A receptacle is allowed on a 15A breaker, but a duplex or multiple receptacles must be 15A.
    Hey, look at the time stamp when I posted!
    I was just shutting down the computer, half asleep, and saw the post.
    Should have waited until I was awake before answering that!
    If you aim at nothing, you will hit it every time!

  4. #24
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,901
    Quote Originally Posted by jim dungar View Post
    You need to reference things in the correct context. Dropping words to prove your point could be disingenuous. 90.1 says it is not a design manual... for untrained persons (my accentuation). IMO, This means that if you are trained (e.g. qualified) you can design using the NEC, if you are untrained don't expect the NEC to teach you.
    The main intent of NEC is still safety of electrical installations, they still cross the line of telling us how to design things quite often when there is little or no impact on safety.

    So I put a 20 amp receptacle on a 15 amp circuit, there is still 15 amp overcurrent protection, where is the safety hazard? If supplying life safety equipment, maybe we have something to be concerned with, but for general use equipment the 15 amp overcurrent does it's job of limiting current on that circuit at the 15 amp level even if there were a 50 amp receptacle connected to it.

  5. #25
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    8,840
    Quote Originally Posted by jim dungar View Post
    You need to reference things in the correct context. Dropping words to prove your point could be disingenuous. 90.1 says it is not a design manual... for untrained persons (my accentuation). IMO, This means that if you are trained (e.g. qualified) you can design using the NEC, if you are untrained don't expect the NEC to teach you.
    You dropped some words, too.

    90.1 - This code is not intended as a design specification or an instruction manual for untrained persons.

    To me, that means the code is not intended to be used as a specification guide, NOR is it to be used as an instruction manual for untrained persons. (Two different things)

    Bear in mind that the wording is of the intent of the code, there is nothing that prohibits the use of the code as a spec guide or as an instruction manual, which is probably why it is done so much.
    Cheers and Stay Safe,

    Marky the Sparky

  6. #26
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,901
    Quote Originally Posted by K8MHZ View Post
    You dropped some words, too.

    90.1 - This code is not intended as a design specification or an instruction manual for untrained persons.

    To me, that means the code is not intended to be used as a specification guide, NOR is it to be used as an instruction manual for untrained persons. (Two different things)

    Bear in mind that the wording is of the intent of the code, there is nothing that prohibits the use of the code as a spec guide or as an instruction manual, which is probably why it is done so much.
    Yes.

  7. #27
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    9,700
    Quote Originally Posted by K8MHZ View Post
    You dropped some words, too.

    90.1 - This code is not intended as a design specification or an instruction manual for untrained persons.
    To me, that means the code is not intended to be used as a specification guide, NOR is it to be used as an instruction manual for untrained persons. (Two different things)
    Bear in mind that the wording is of the intent of the code, there is nothing that prohibits the use of the code as a spec guide or as an instruction manual, which is probably why it is done so much.
    I included an ellipse in order to indicate words were omitted, I then accentuated the words which I think go together, because without commas being used it is likely the grouping of adjectives is intended to be 'design and instruction' rather than 'design and untrained'. Both design and instruction modify an item, 'manual' while, untrained modifies an individual.

    The word 'specification is not in 90.1, regardless, what purpose is the NEC intended for if it cannot be used as a guide for creating a design? Are we supposed to blindly install stuff then hope that it complies with the code?
    90.1 effectively says the intent of the NEC is not to make a person 'not be untrained'. Following only the NEC will likely not result in a safe installation. The NEC is a 'what must be done' not a 'how to do it' standard.
    Just because you can, doesn't mean you should.

  8. #28
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    8,840
    Quote Originally Posted by jim dungar View Post
    The word 'specification is not in 90.1,
    I think it is....(C) Intention. This Code is not intended as a design specification or instruction manual for untrained persons.

    regardless, what purpose is the NEC intended for if it cannot be used as a guide for creating a design?
    (A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity.

    Are we supposed to blindly install stuff then hope that it complies with the code?
    You install stuff based upon your training and experience and do it to suit the situation. The code is consulted to assure that the bare minimum legal standards have been met.

    (C) Continued - Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.

    90.1 effectively says the intent of the NEC is not to make a person 'not be untrained'. Following only the NEC will likely not result in a safe installation. The NEC is a 'what must be done' not a 'how to do it' standard.
    Following only the NEC will certainly provide for a safe installation, but that's all. See (C) continued.

    As I stated earlier, nothing says that using the NEC as a spec guide or a training manual is prohibited. If a person wants to use a book that explicitly states the book's intent is NOT to be used as a spec guide or training manual is up to the user. Sticking strictly to the NEC will provide an installation that is, basically, the worst allowed by law.
    Cheers and Stay Safe,

    Marky the Sparky

  9. #29
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,269
    A 20 amp outlet on a 15 amp circuit and breaker is considered deceiving. If the home owner is out shopping for treadmills. They may look at the male plug (with one prong turned side ways) and say oh we have those.

  10. #30
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    8,840
    Quote Originally Posted by kwired View Post
    This is what I get for posting before confirming - Table 210.21(B)(3) pretty much says a 15 amp circuit can not have over a 15 amp receptacle on it.

    IMO there is little harm in putting a 20 amp receptacle on a 15 amp circuit and this is another case of NEC being the design manual it says it is not in 90.1
    That table only applies to "two or more receptacles or outlets".
    Cheers and Stay Safe,

    Marky the Sparky