Results 1 to 7 of 7
Thread: Bar equipment
  1. #1
    Join Date
    Jul 2015
    New York, NY
    Posts
    171
    Bar equipment
    Hi all,
    I'm working on a demand load calculation for a restaurant that has a kitchen in the back, with over 15 pieces of equipment, and a bar in the front area for drinks. Looking at the NEC 2008 version, can the equipment in the bar area be included in the demand loads of table 220.56? I'm thinking of using 65% demand for the kitchen and the bar, but i'm not sure if the bar area can be included.
    According to the 2008 NEC, a kitchen is defined as: An area with a sink and permanent facilities for food preparation and cooking. so i don't think a bar applies. if not, what demand can i use for the bar section?
    Thanks.
  2. #2
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    If the bar has "commercial electric cooking equipment, dishwasher booster heaters, water heaters, and other kitchen equipment" (which the "other kitchen equipment" is pretty vague, then I don't see why you can't apply those demand factors to any common feeder or service that supplies both areas. A feeder that only supplies the bar or only supplies the kitchen can't use the total appliances in both areas for demand factors, but the service or feeder that supplies both certainly should be able to.
  3. #3
    Join Date
    Jul 2015
    New York, NY
    Posts
    171
    Quote Originally Posted by kwired View Post
    I see what you're saying... in this case the bar has 'other kitchen equipment'. it doesn't have electric cooking equipment, dishwasher booster heaters, or water heaters. However, 'other kitchen equipment' by definition is an area with a sink with permanent facilities for food preparation and cooking... the bar is not used for food prep or cooking, which is what throws me off.
    I think i'm splitting hairs... i'll just apply the 65% demand!
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    Quote Originally Posted by Grouch1980 View Post
    A majority of the bar load is probably refrigeration type equipment, correct? I could be reading between the lines but see no problem with using the same demand factor to any common service or feeder equiment. You could easily put same or similar refrigeration equipment in the kitchen area and have no reading between the lines then.
  5. #5
    Join Date
    Jul 2015
    New York, NY
    Posts
    171
    yes, it's mostly refrigeration equipment at the bar. Nothing cooking related. Thanks kwired!
  6. #6
    Join Date
    Aug 2008
    Posts
    376
    So Refrigeration equipment in the kitchen can be counted and used with the demand factors of 220.56? Most food that is cooked is frozen or refrigerated before you cook it So refrigeration is part of kitchen equipment?
  7. #7
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,050
    Quote Originally Posted by arnettda View Post
    Yes, read the sentence in that section that includes thermostatically controlled equipment.
    "Electricity is really just organized lightning." George Carlin
    Derek
Posting Permissions
  • You may not post replies
  • You may not edit your posts