Page 2 of 3 FirstFirst 123 LastLast
Results 11 to 20 of 25
Thread: Siemens Two Pole AFCI Circuit Breaker
  1. #11
    Join Date
    Mar 2003
    New England
    Posts
    13,263
    Quote Originally Posted by chris1971 View Post
    Thanks for the information I appreciate it.
  2. #12
    Join Date
    May 2011
    Posts
    4,122
    Quote Originally Posted by peter d View Post
    Did you miss that this is a 2 pole breaker?
    Surely you're not suggesting that single-phase line-line loads are never installed on three phase systems.
  3. #13
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,980
    Is this a trick question? It's 208.
    Yes so why did you say they were dp breakers. Someone can wire an apt with multiwire branch circuit and be stuck with needing dp breakers. I was surprised that if you wanted to add afci on an existing multiwire branch circuit that you could not do it in apts feed with 208V
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #14
    Join Date
    Mar 2003
    New England
    Posts
    13,263
    Quote Originally Posted by jaggedben View Post
    The question was whether or not a specific brand 2-pole AFCI would work on a 208 volt system.
  5. #15
    Join Date
    Mar 2003
    New England
    Posts
    13,263
    Quote Originally Posted by Dennis Alwon View Post
    Because the double pole AFCI is limited to 120/240 volt circuits. We're arguing the same thing.
  6. #16
    Join Date
    Nov 2015
    Ellington, CT
    Posts
    29
    The only manufacturer that gives you a way out on a 120/208 panel that has MWBCs in it is G.E. and their Mod 3 breaker. You use two single pole breakers with their handle tie. Wire it to their spec, it is U. L. listed for that use.
    Sent from my XT1254 using Tapatalk
  7. #17
    Join Date
    May 2011
    Posts
    4,122
    I think Dennis' question is still unanswered though. If you're required to have AFCI breaker on a 2-pole circuit and the panel happens to be 208V, are you SOL if you didn't think to install a GE panel (per bsmith8691)?
  8. #18
    Join Date
    Mar 2003
    New England
    Posts
    13,263
    That seems to be the case.
  9. #19
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,980
    If you are adding a new circuit you obviously would not use a multiwire branch circuit and if you are extending the circuit then use an afci Receptacle. Probably not a problem.
    I guess knowing this is good info for planning
  10. #20
    Join Date
    Mar 2007
    Valdosta, GA
    Posts
    3,961
    Quote Originally Posted by bsmith8691 View Post
    But how do you connect the neutral of a MWBC?
    Brought to you by Carl's Jr.