    Repurposing an 8/2 wire...

    So my friend has an old 8/2 SER cable that used to service an A/C which has been removed. She wants to install a hot tub and wants to know if I can reuse the circuit. Would it be safe to relocate the bare wire to the neutral bar (after wrapping the bare exposed wiring with white phase tape) to supply a neutral to the spa panel? I could then drive a ground rod within 6 feet of the GFCI spa panel to supply the earth ground. Would this be considered safe? This is my first time dealing with/thinking about a situation like this... Thanks.

  2. #2
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,135
    NO do not do that. The grounding rod will not clear the fault and the breaker will not open up.

    Why do you need a neutral for the spa?
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  3. #3
    Join Date
    Apr 2014
    Location
    Benicia, CA, USA
    Posts
    42
    Quote Originally Posted by edward View Post
    NO do not do that. The grounding rod will not clear the fault and the breaker will not open up.

    Why do you need a neutral for the spa?
    I actually don't need it for the spa, I need it for the GFCI to function properly, correct?

  4. #4
    Join Date
    Apr 2014
    Location
    Benicia, CA, USA
    Posts
    42
    Click image for larger version. 

Name:	5.JPG 
Views:	380 
Size:	56.0 KB 
ID:	17185

  5. #5
    Join Date
    Apr 2014
    Location
    Benicia, CA, USA
    Posts
    42
    Proposed idea:

    Click image for larger version. 

Name:	5.JPG 
Views:	468 
Size:	67.7 KB 
ID:	17186

  6. #6
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    4,186
    Unless the spa is very small (2 person), 8/2 with ground will likely not be enough ampacity for the circuit. 2p GFCI discos for 240V spas need a ground, not a neutral, and most will be 50A. Spas have to be sized 125% of the circuit ampacity. The spa mfg instructions may preclude your proposed install. I'll have to look further in article 680 to see if there are more problems (code violations) here in the am.

    eta: a separate ground rod at the spa in lieu of a grounding conductor is neither safe nor code compliant. You cannot use USE/SER directly to the spa, maybe to the disco, but from there to the spa has to be an approved wiring method as described in article 680. Typically, even in SF residences, that is LFNMC or RPVC with individual conductors. You cannot run the existing cable directly to the spa; it must have a disconnect within sight of the tub that is >6' but less than 25' from the spa.
    Last edited by JFletcher; 03-29-17 at 01:26 AM.
    Electricians do it until it Hertz!

  7. #7
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,127
    Quote Originally Posted by EEEC View Post
    I could then drive a ground rod within 6 feet of the GFCI spa panel to supply the earth ground.
    It is very important to understand why that not only doesnt work, but is dangerous. I suggest reading this sticky:


    http://forums.mikeholt.com/showthread.php?t=95495
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  8. #8
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,135
    Quote Originally Posted by EEEC View Post
    Proposed idea:

    Click image for larger version. 

Name:	5.JPG 
Views:	468 
Size:	67.7 KB 
ID:	17186

    NO
    do not do this.

    Assume there is fault between line 1 and the frame of the motor. Now, use yoru finger and folow the grounding wire back to the source where does the ground fault go? To the ground!!

    That will NOT break the circuit breaker, because there is no electrical connection between the ground rod and the main grounding buss.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  9. #9
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by electrofelon View Post
    It is very important to understand why that not only doesnt work, but is dangerous. I suggest reading this sticky:


    http://forums.mikeholt.com/showthread.php?t=95495
    Thank you Ethan.

  10. #10
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by EEEC View Post
    Would this be considered safe?
    Absolutely no.

    It is dangerous.