Results 1 to 3 of 3
Thread: Pv system on multifamily
  1. #1
    Join Date
    Sep 2011
    woodbridge, ct. USA
    Posts
    931
    Is there a way to install a pv system on a 3 fam house that accounts for the entire load but also maintains individual metering and is acceptable to the POCO
    Sent from my SM-G930V using Tapatalk
  2. #2
    Join Date
    May 2011
    Posts
    3,552
    You've got to talk to the POCO and/or your state and local regulators.
    In California there is a provision to add a new meter for the solar system and apportion the production among the existing meters on the same service by mutual agreement of the customers on the existing meters. This is a law that was passed by the legislature. There are significant costs and for 3 meters it tends on the side of not being cost-effective.
    If your locality doesn't have a similar provision then you'll have to install three systems.
  3. #3
    Join Date
    Sep 2011
    woodbridge, ct. USA
    Posts
    931
    Quote Originally Posted by jaggedben View Post
    Thanks, will be talking to them next week.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts