    Using PV disco for chase

    I have 2 solaredge inverters, 1 string per inverter. Can I use one of the inverters integrated DC dico to chase the other inverter source CKT threw. Thanks

  2. #2
    Join Date
    May 2011
    Posts
    3,548
    In my opinion there's no code violation there, although it seems like poor practice if it's just a shortcut and there's not a true difficulty in doing it another way.

    (What I would not do is run one inverters AC output through another inverter's disco. 690.31(B)).