    Plumbing related

    I need your help. For unknown reasons I cannot log in the plumbing forum. I an dealing with a General inspector from the city in several items related to electrical upgrades, gas upgrades and a situation with a vent stack. as this inspector is a "general" he is not well versed in specifics. AND, I need your help in "wording" with him (you know that my English sucks)

    I questioned an electrical and gas upgradeds made from someone else that was approved by this inspector, I questioned him and the city didn't have another alternative that backtrack and redo the entire situation.

    So, I questioned a vent stack that is located between 2 mobile homes. That vent stack is too short and residents of those 2 mobile homes, specially in summer, cannot open their bedroom windows and those gases leak into ... (sewer gases can be hydrogen sulfide, ammonia, methane, esters, carbon monoxide, sulfur dioxide and nitrogen oxides)

    I know that you don't deal with plumbing, but please help me with the wording as this inspector is disappointed with me as he had to backtracked in the gas and electric.

    He is stating that this sewer stack is "grandfathered" as it is in this way for the last 20 years. I don't find the wording to tell him that "ANY grandfathered hazards has to be corrected" and that stack (the black pipe in the photo) needs to be raised at least 2', see how close is to the bedroom windows. It is ok if this stack is on the top of the home but not on the side.

    Can you help with the wording?
    Attached Images Attached Images  

  2. #2
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,472
    You run into some real deals. I have never seen an installation like this nor do I understand why this is needed if the plumbing is done correctly in each MH. Granted I never looked, but HS, what Cluster F.

    I can make stuff run down hill and know payday is on Friday but otherwise I am not a plumber
    Tom
    TBLO

  3. #3
    Join Date
    May 2006
    Posts
    448
    What is "HS, what Cluster F"

    All mobile parks have their sewer system and the mobile homes have their own, so a mobile home comes into the park and hook up. Beside a good draining system the vents have to be far away horizontally and vertically to avoid gases. Because this inspector is pi...off, he is telling me that it is "grandfathered".

    I am writing again to the city but I cannot find the technically words to say that an hazards must be corrected regarding grandfathering or not. As I said above the city had to ordered a "redo" on the gas and electrical issue after it passed inspection.

    "You run into some real deals", you are right, the problem is that I have too many licenses and I have no other choice that to put my nose into. See photo, I blackened for obvious reasons, I have strong accent/vocabulary but I don't think with accent, but many times I have difficulty in communicating. Old parakeet never learn to talk ..

    I am a not a yes man and this is one of the many times I challenged (right word?) inspectors in VA, WA and AZ but at the end we respect each other.
    Attached Images Attached Images  

  4. #4
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,472
    Hint: Don't use HS or CF in your correspondence.

    "Holey Smokes" and "Cluster Fix" are close enough for polite company.
    Tom
    TBLO

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,350
    Seems it should be supported by something more mechanically sound then it is. Add a couple more feet to the height and things only will get worse, at least here where the wind does blow at least 300 out of 365 days a year.

  6. #6
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,408
    Quote Originally Posted by ptonsparky View Post
    You run into some real deals. I have never seen an installation like this nor do I understand why this is needed if the plumbing is done correctly in each MH. Granted I never looked, but HS, what Cluster F.

    I can make stuff run down hill and know payday is on Friday but otherwise I am not a plumber
    That makes two of us.

    Raising the vent stack a few feet will make no appreciable difference in gasses being noticeable, nor reducing their concentration. H2S is detectable by the nose at like half a part per billion. You're not going to reach LEL concentrations, but the odors are going to be objectionable while there is a straight stack sans P/S trap on a main waste line. Is their waste going to city sewer or a septic tank/field?

    I suppose that vent *could* be a vacuum break only, to keep from siphoning out the water in traps when the septic tank is drained, and is not operating properly, but that is a wag (wild a** guess).

    I heard a long time ago a saying, which is completely wrong, in waste water treatment: the solution to pollution is dilution. In this case, the MH owners may be able to reduce to gasses by running more water, tho it's only a stop-gap measure to the proper fix, which they nor the park owner are going to want to pay for.

    eta: I realize the vents on top of houses are susceptible to positive pressure and venting, but they are mainly siphon breaks to keep you from sucking the water out of your traps when you flush a toilet, use a sink, etc. Maybe going up another 10' on the stack would work...
    Electricians do it until it Hertz!

  7. #7
    Join Date
    May 2006
    Posts
    448
    Ok, I know that as I talk too much I write too much too, and I always confuse things out. If the windows are open, specially in hot days, the "smell of gases/sewer" enter the house and that is not acceptable. Dealing with the inspector to give notice to the owner for the correction, the inspector calls this situation a "grandfather situation" and In my opinion, any hazard is NOT grandfathered. He tried with the same with the gas meter and with the electrical "repair" BUT I questioned and the city agreed to REDO. Of course, this inspector is P.. off, but I don't care and never care for incompetent inspectors, inspectors that are now "general inspectors" and have very limited knowledge of electrical. plumbing and mechanical.

    Attached is the gas meter photo, see how the flex is stressed out where is connected to the outlet and it over time will leak and will cause explosion, is that a grandfathered too? This is the same MHP that I posted in another post the electrical and that is not grandfathered neither. They are coming to meet with me and I want to have the right wording of: Hazards are not grandfathered!

    That vent stack has to be raised and has to has better support.

    Next post I will post the electrical again, I know that some of you don't agreed with me, but I saw and see too many fires caused by incompetent workers and inspectors and I have probe of that.
    Attached Images Attached Images  

  8. #8
    Join Date
    May 2006
    Posts
    448
    Hello kwired, I just notice that you have posted over 30,000 posts, whoa! You are a good mentor. Are you the one with more posts? Reading all the posts in this forum give the readers a lot of "free training" and that is priceless! This forum has at least 1,000 years of experience, maybe someone can take the time and multiplied the members by the hours and find how many years of experience really this forum offer.

  9. #9
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    20,307
    Quote Originally Posted by JFletcher View Post
    eta: I realize the vents on top of houses are susceptible to positive pressure and venting, but they are mainly siphon breaks to keep you from sucking the water out of your traps when you flush a toilet, use a sink, etc. Maybe going up another 10' on the stack would work...
    On the first part, I have to ask if you know why p/s traps are installed in drain lines in the first place? Vents may be a siphon break, but there's a reason for the location of their (i.e roof stacks) opening to atmospheric air being at least 2' higher than anything within a 10' radius*.


    *Requirements vary by jurisdiction.
    I'll never get there. No matter where I go, I'm always here.

  10. #10
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,408
    Quote Originally Posted by Smart $ View Post
    On the first part, I have to ask if you know why p/s traps are installed in drain lines in the first place? Vents may be a siphon break, but there's a reason for the location of their (i.e roof stacks) opening to atmospheric air being at least 2' higher than anything within a 10' radius*.


    *Requirements vary by jurisdiction.
    Plumbing drain vents are for allowing air to be sucked into a system when you, say, flush a toilet. If there is no venting, the water going down the drain can create a vacuum on the entire system, which can suck out the water in sink and tub p-traps, and then allow sewer gasses to enter a dwelling.

    Vent pipes here are located on the roofs of structures (houses), but they are not always at the high point, and typically there is roofline nearby and higher than the vent stack.

    I mistyped my reply earlier in that there are no p or s traps in a vent stack, I meant the drain system in general. A trap in a vent pipe negates its purpose.