    3 Phase GFCI for portable tools

    I have a concrete cutting contractor that requires a 3 Phase GFCI 20 amp for his portable wet cutting saw, he's using a gas powered generor for the supply. Is there such a device on the market that can trip out at 5ma?

    Also can the GFCI work without a load neutral?
    Thanks,
    Ian Reece, Ontario Canada

  2. #2
    Join Date
    Mar 2010
    Location
    Lake of the Ozarks
    Posts
    983
    Check Bender.org They have tons of GFCI and GFP options. I would not have thought that 5mA would be appropriate for this application but I do not know.

    http://www.bender.org/products_list....FVa1wAodDwIJcg

    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.

  3. #3
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,015
    5mA isn't likely going to work, but it's probably not required either. There is a whole new class of GFCIs now for things like this, read this article and see which class of GFCI applies, then do a search for that class of GFCI. Most mfrs have released products now to fill this requirement.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  4. #4
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,826
    Quote Originally Posted by Jraef View Post
    5mA isn't likely going to work, but it's probably not required either. There is a whole new class of GFCIs now for things like this, read this article and see which class of GFCI applies, then do a search for that class of GFCI. Most mfrs have released products now to fill this requirement.
    Where is the article?
    If Billy Idol or John Denver is on your play list go and reevaluate your life.

  5. #5
    Join Date
    Jul 2012
    Location
    cyberspace
    Posts
    163

    Extension Cord

    I have the same question. I came across a portable machine, 3phase. 208v 20a extension cord that is ran outside the building. L15-20 twist lock extension cord, 100' long. 14-4 or 12-4 extension SJ cord. They wheel the machine outside on nice days, and cut material. Does this need a GFI ?

    Is there a 3 phase GFI that will work with a motor starter?

  6. #6
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,015
    Quote Originally Posted by ActionDave View Post
    Where is the article?
    Oops, sorry, never noticed that the link wasn't there!

    http://www.csemag.com/single-article...1d51ba57a.html
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  7. #7
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,446
    Quote Originally Posted by Jraef View Post
    Oops, sorry, never noticed that the link wasn't there!

    http://www.csemag.com/single-article...1d51ba57a.html
    Small typo: "NEC requires them on all 5-amp and 20-amp 125-V utility outlets used in locations such as ....",
    and the flow chart path to Class C does not properly represent the AND logic.