Results 1 to 7 of 7
Thread: 3 Phase GFCI for portable tools
  1. #1
    Join Date
    Apr 2017
    400-5110 Creekbank Road, Mississauga, ON. L4W 0A1
    Posts
    1
    I have a concrete cutting contractor that requires a 3 Phase GFCI 20 amp for his portable wet cutting saw, he's using a gas powered generor for the supply. Is there such a device on the market that can trip out at 5ma?
    Also can the GFCI work without a load neutral?
    Thanks,
    Ian Reece, Ontario Canada
  2. #2
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,027
    Check Bender.org They have tons of GFCI and GFP options. I would not have thought that 5mA would be appropriate for this application but I do not know.
    http://www.bender.org/products_list....FVa1wAodDwIJcg
    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.
  3. #3
    Join Date
    Jul 2006
    Posts
    7,567
    5mA isn't likely going to work, but it's probably not required either. There is a whole new class of GFCIs now for things like this, read this article and see which class of GFCI applies, then do a search for that class of GFCI. Most mfrs have released products now to fill this requirement.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  4. #4
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,392
    Quote Originally Posted by Jraef View Post
    Where is the article?
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  5. #5
    Join Date
    Jul 2012
    cyberspace
    Posts
    163
    Extension Cord
    I have the same question. I came across a portable machine, 3phase. 208v 20a extension cord that is ran outside the building. L15-20 twist lock extension cord, 100' long. 14-4 or 12-4 extension SJ cord. They wheel the machine outside on nice days, and cut material. Does this need a GFI ?
    Is there a 3 phase GFI that will work with a motor starter?
  6. #6
    Join Date
    Jul 2006
    Posts
    7,567
    Quote Originally Posted by ActionDave View Post
    Oops, sorry, never noticed that the link wasn't there!
    http://www.csemag.com/single-article...1d51ba57a.html
  7. #7
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,079
    Small typo: "NEC requires them on all 5-amp and 20-amp 125-V utility outlets used in locations such as ....",
    and the flow chart path to Class C does not properly represent the AND logic.