Trailered 3-phase generator: How many conductors needed for power cable?

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Watch out for mechanical forces between conductors during motor starting if you use separate wires, regardless of connector type. Current could be up to the full surge of the generator. :)
 

iwire

Moderator
Staff member
Location
Massachusetts
Watch out for mechanical forces between conductors during motor starting if you use separate wires, regardless of connector type. Current could be up to the full surge of the generator. :)

I have never seen them move and I have done a lot of temp gensets with single conductor.

It might get exciting during a line to line short but will a single generator really have a high short circuit current?


f127040d.jpg


4c39e387.jpg


201ce25b.jpg


Now2.jpg


Now3.jpg


Sometimes speed is more of an issue than neatness ...

EroomDoor.jpg
 

ron

Senior Member
I have never seen them move and I have done a lot of temp gensets with single conductor.

It might get exciting during a line to line short but will a single generator really have a high short circuit current?

That is my experience as well.

If the subtransient reactance (x") of the alternator was 10%, then you would get 10 x FLA out during a bolted fault.
 