Bonding conductor size at J-Box

Status
Not open for further replies.

yfz450rr

Member
If I'm running #10 conductors due to voltage drop from a 20A overcurrent device, would I be able to use a #12 bonding jumper at a j-box? All conductors are #10 including the EGC. Table 250.122 shows a #12 copper for a 20A Overcurrent Device. Just want to know if I can use a #12 bonding to the box or I would have to use the same size (#10) as the Equipment Grounding Conductors.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Art. 50.102(D) states that the bonding jumper be sized according to Table 250.122. It does not state that it must be upsized as the equipment grounding conductor is required in 250.122(B). I am not sure that is the intent but that is what is stated
 

Smart $

Esteemed Member
Location
Ohio
Art. 50.102(D) states that the bonding jumper be sized according to Table 250.122. It does not state that it must be upsized as the equipment grounding conductor is required in 250.122(B). I am not sure that is the intent but that is what is stated
I believe the proper section is 250.148.

IMO, the jumper is an EGC per the mentioned section... not an EBJ under 250.102(D)... so #10 would be required.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't see where 250.148 states we must size it to the upsized wire size. I think that is the intent but I don't see the wording to support it.
 

Smart $

Esteemed Member
Location
Ohio
I don't see where 250.148 states we must size it to the upsized wire size. I think that is the intent but I don't see the wording to support it.
Read between the lines. :D

250.148 says the EGC must be connected to the box or through a permitted device (essentially, don't have that section open currently).
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You are pulling all #10s, you are not using #12, why would you even think about the size of the jumper?...just use some of the scrap #10. Codewise, as seen from the previous posts, the code is not clear.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What is the bonding jumper being used for? If it's from the receptacle to a metal box you could use #12 if the device had #12 pigtails.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You are pulling all #10s, you are not using #12, why would you even think about the size of the jumper?...just use some of the scrap #10. Codewise, as seen from the previous posts, the code is not clear.

I agree but I am thinking the OP wants to use #12 because it is easier then the very rigid #10
 

yfz450rr

Member
I agree but I am thinking the OP wants to use #12 because it is easier then the very rigid #10

Yes, using #12 is much easier than trying to bend a #10 solid or using a crimp terminals. But I guess another way to look at it, with the #10 you can change to a 30A overcurrent device, so #10 jumper would be required. Thanks for all the good answers.
 

Smart $

Esteemed Member
Location
Ohio
If it's a 20 amp circuit how could you change to a 30 amp OCPD?
He's using #10 to compensate for voltage drop. The circuit OCPD can be changed to 30A and still be compliant (in general)... but the voltage drop would not change for the same load.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I still don't see how you can take a circuit that needs a 20 amp OCPD and just throw in a 30 amp because the conductors are big enough. :?
 

Smart $

Esteemed Member
Location
Ohio
I still don't see how you can take a circuit that needs a 20 amp OCPD and just throw in a 30 amp because the conductors are big enough. :?
I agree, the load or purpose of the circuit may prevent doing so from being compliant.. but in general it is not prohibited.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I still don't see how you can take a circuit that needs a 20 amp OCPD and just throw in a 30 amp because the conductors are big enough. :?


Well we don't know what the load is and in some case a 30 amp overcurrent protective device would be compliant.. 210.23(B)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, the load or purpose of the circuit may prevent doing so from being compliant.. but in general it is not prohibited.

It sounded to me like he was concerned that someone else would see #10 conductors and change the OCPD to 30 amps.
 

yfz450rr

Member
It sounded to me like he was concerned that someone else would see #10 conductors and change the OCPD to 30 amps.

That's correct infinity. I will not change it to a 30A breaker, but who knows what the facility electrician would do in the future. The load is only a 20A general use receptacle, but if they bring a piece of equipment that requires a 30A circuit, then they might use it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That's correct infinity. I will not change it to a 30A breaker, but who knows what the facility electrician would do in the future. The load is only a 20A general use receptacle, but if they bring a piece of equipment that requires a 30A circuit, then they might use it.

That would be fine if they changed all of the components of the circuit to 30 amps. We use #10 on 20 amp circuits all of the time so to me it's not an issue. Anyone competent electrician would not simply remove the 20 amp OCPD and replace it with a 30 amp OCPD.


I have heard of inspectors who turned down jobs because of that. Easy fix-- put a tag on it.

They need a refresher course. :roll:
 

jap

Senior Member
Occupation
Electrician
That would be fine if they changed all of the components of the circuit to 30 amps. We use #10 on 20 amp circuits all of the time so to me it's not an issue. Anyone competent electrician would not simply remove the 20 amp OCPD and replace it with a 30 amp OCPD.

:roll:

On that same note,,,,, I know a lot of competent electricians that would not chase #10's all the way to the end of the run to see if it was all #10 prior to slapping in a 30 amp breaker.;)

Also, most of the premade ground stingers with the screws you'd purchase at the supply house are mostly #12 not #10, so the question of the need for #12 or #10 bonding jumpers for a #10 ground wire that may happen to be in the box brings up an interesting point. Would a #12 Ground Stinger not do its job on a 30 Amp circuit?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
On that same note,,,,, I know a lot of competent electricians that would not chase #10's all the way to the end of the run to see if it was all #10 prior to slapping in a 30 amp breaker.;)

I wouldn't call anyone who would do that competent.:eek:hmy:
 
Status
Not open for further replies.
Top