Thread: Grid tied backup generator

  1. #21
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    4,737
    Quote Originally Posted by GoldDigger View Post
    Rectify the generator output to DC and feed a grid tie inverter? Not sure how to handle the MPPT input though.

    Sent from my XT1585 using Tapatalk
    OK, hadn't thought about that. Beyond that, unless you are getting a lot more than fuel cost and depreciation for the feed in, I doubt it would be economic. Of course, in Spain some solar producers were using grid power for lights mounted above solar panels or making a direct connection, it isn't clear which. Only possible because the feed-in tariffs were so freakishly high.

  2. #22
    Join Date
    Feb 2008
    Location
    Texas
    Posts
    877
    Quote Originally Posted by gadfly56 View Post
    At that size, I seriously doubt any BPU will entertain a grid tie to push power into the grid, not the least because I doubt your standard 11 KW Generac comes with any provision for syncing with the grid, and such an option if available would likely be many times the cost of the generator itself. Also, I'm sure the manufacturer would walk/run away from having anything to do with this lash-up.
    I figured the job would require an other-than-Generac ATS, probably be a closed-transition with some means to sync with the utility. The economy of this experiment is not an issue (to a certain point, of course) but more of a how would this be done exercise. Whether any kind of switch could be had for a <100A, 1-phase application, remains to be seen.

  3. #23
    Join Date
    May 2011
    Posts
    3,776
    Quote Originally Posted by GoldDigger View Post
    Rectify the generator output to DC and feed a grid tie inverter? Not sure how to handle the MPPT input though.
    Use a non-MPPT charge controller on a battery inverter such as an Outback? Not sure Outback will support that, maybe there's another. Just brainstorming.

  4. #24
    Join Date
    Nov 2016
    Location
    Dublin, GA
    Posts
    160
    I doubt that there is a POCO anywhere in the country that would permit such a small installation. However, to answer the question it canceratinly be done - if cost is no object.

  5. #25
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,429
    The way the off line generators were synched at power plant I worked at was the generators acted like motors and started spinning in synch with the grid. Once the prime mover 'caught up', the motor/generator was then used as a generator. This was at a peaker using NG.
    Cheers and Stay Safe,

    Marky the Sparky

  6. #26
    Join Date
    Feb 2008
    Location
    Texas
    Posts
    877
    The normal set-up I have come across are:

    Poco----ATS----Generator
    .............|
    ...........Home

    or

    Solar----------------Home
    ......................|
    Generator---Batteries

  7. #27
    Join Date
    May 2011
    Posts
    3,776
    If economy is not an issue then I believe the most straight foward option on the market, if the goal is to have both grid exports and backup power, is solar plus batteries. There have been systems around for a while that allow the generator to be synced up to that, but only when in back up mode, not for the generator to feed the grid.

  8. #28
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    8,489
    Quote Originally Posted by jaggedben View Post
    If economy is not an issue then I believe the most straight foward option on the market, if the goal is to have both grid exports and backup power, is solar plus batteries. There have been systems around for a while that allow the generator to be synced up to that, but only when in back up mode, not for the generator to feed the grid.
    In that case, however, it's the solar/battery inverter synching with the generator, not the other way around.

  9. #29
    Join Date
    May 2011
    Posts
    3,776
    Quote Originally Posted by ggunn View Post
    In that case, however, it's the solar/battery inverter synching with the generator, not the other way around.
    Well... exactly. The generator doesn't do the syncing.