    Out of the thousands of keypads we install, maintain,and troubleshoot, about 6 are getting complaints of being shocked.
    I immediately thought of static,because they are in their cars. The keypads are attached to a 10"×1/4" steel bollard. They're sunk 2' in the ground and surrounded by 2' sqare and deep of concrete.
    Double, triple grounded it,but no success.
    Any ideas?
    Last edited by GoldDigger; 04-19-17 at 05:46 PM. Reason: No Edit, just testing....
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,071
    It is, IMHO, one hundred percent certain that it is static. Perhaps related in some way to the pavement and other conditions as the cars approach the keypad.
    If it were foreign voltage of any sort on the keypad, you would be able to measure it relative to local or remote ground.
    If people were standing on dirt or concrete next to the bollard, then there would be a possibility that there was a step potential in the earth surrounding the bollard because of fault current in the earth for some reason. But if they are in a car that would not be noticed and would not cause a "shock".
    Is it a single spark at first touch? Or is it a repeated sensation for as long as they are in contact with the keypad?
  3. #3
    Join Date
    Mar 2007
    Valdosta, GA
    Posts
    3,929
    Are you measuring any voltage at the keypad?
    I had this happen once (it was a Detex alarm shocking people when they put the key in), and read a small amount of voltage, and only after it rained.
    Found a cracked section of conduit underground about 5' away, and the insulation had deteriorated off the conductors. I had kneeled down on the ground while looking for the source and it knocked the piss out of me when I touched the concrete sidewalk.
    Brought to you by Carl's Jr.
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,680
    Not necessarily a permanent solution, but water down the driveway to see if that helps, it should lower static charge on vehicles as they approach if that is the problem.