    Here's a good one. One of the POCO guidelines says "Pull boxes or tap boxes are prohibited except when located next to and installed as part of the service equipment." Another electrician told me the POCO field rep came out to spot a meter location for him and told him he couldn't use an LB to go around a corner of the house. Apparently they consider it a theft issue, (like if you put in a T and ran something into the attic I guess). I don't see how they could enforce that as they do not own anything attached to your house. The electrician said he's never used SEU cable but now thinks he has to.
  2. #2
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,452
    Here just two weeks ago we piped out of a 2000 amp 480v EUSERC section to a 121413 meterbase and had an LB in the run. We were told by the POCO meterman to remove it, someone could steal power. I did not ask why someone would fool around with some #12's feeding a meterbase when they could just as easily clip onto 2000 amp bussbars and steal some real power.
    Of course, we repiped it without the LB.
    After we redid it, it was mentioned that a guy might be able to find a special LB cover or use different screws through it that a meterman could run his lock through to secure it. I haven't investigated it though.
  3. #3
    Join Date
    May 2011
    Posts
    3,948
    Quote Originally Posted by GerryB View Post
    People who would steal would not put in a T. Of course people who would steal might not be discouraged by the lack of an LB, and just take an angle grinder to it even if it's RMC. But an LB certainly could make their task quite a bit easier.
    It does baffle me a bit if SEU is considered more secure against theft.
  4. #4
    Join Date
    Oct 2015
    US
    Posts
    417
    The Poco here will allow us to use a trough or a wire way before the meter as long as the cover is fastened in place with tamperproff screws . It's pretty hard not to have some sort of splice poo t before a meter here since the Poco will only allow you to tap the end box a maximum of 2-3 times depending on it's size
    Sent from my SM-G935P using Tapatalk
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,831
    Quote Originally Posted by jaggedben View Post
    Baffles me a lot. If I were to make an illegal tap I would welcome having SE cable instead of a metal raceway to tap into.
  6. #6
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,972
    Find your POCO Guidelines they usually determine the service point in which they control the service conductors -- they do have the right not to energize -- should always check with POCO prior to digging lateral ditch or dig around the home extending the underground run
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  7. #7
    Join Date
    Sep 2011
    woodbridge, ct. USA
    Posts
    1,030
    Quote Originally Posted by mwm1752 View Post
    Those were the POCO guidelines I quoted and from the posts and talking to others I guess not too crazy from their point of view. I did talk to a POCO field guy today and he hemmed and hawed a little and "kinda" indicated it might be a case to case determination. When I said sometimes it an aesthetic thing he bluntly said, "We don't care about aesthetics"
  8. #8
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Less secure physically but more obvious visually.
    I will have achieved my life's goal if I die with a smile on my face.
  9. #9
    Join Date
    Mar 2003
    New England
    Posts
    13,190
    The neutral is tightly wrapped around se cable, it's certain explosion time if you tried to tap into it.
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,831
    Quote Originally Posted by peter d View Post
    Strip enough sheath off or even cut the neutral if necessary (best not to do so under load) and splice it together again and it will be much easier then making a tap in a conduit body. But we are not here to help people steal power, so I never said that