Thread: Voltage between line to neutral and line to ground

  1. #11
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,120
    Quote Originally Posted by GoldDigger View Post
    But the OP reports 17 volts between the neutral and the line downstream of the open breaker. To me that suggests phantom voltage on the ungrounded conductor, not an offset between neutral and ground.
    Other than in the title the OP never refers to ground (EGC?) at all.

    Sent from my XT1585 using Tapatalk
    I don't know what I was looking at before, I think the title was throwing me off, for some reason I thought he was reading 17 volts between neutral and ground. I don't see it that way now and do suspect phantom voltage is what he has.

  2. #12
    Join Date
    Jul 2012
    Location
    Riyadh Saudi Arabia
    Posts
    92
    i am checking all the possibilities on site that are highlighted by forum member, and will come back to the forum with the exact solution of the problem when rectified.