Page 2 of 5 FirstFirst 1234 ... LastLast
Results 11 to 20 of 49
Thread: Detect The Violations - Electrical Panel
  1. #11
    Join Date
    Apr 2017
    Florida
    Posts
    45
    Perhaps these close up shots with the video may give you a better visual inspection.
    I'm very appreciative folks, how have I not known about this forum sooner? I just kill myself looking for answers at times for items I just can't find or understand by way of some complicated NEC jargon.
    Click image for larger version.
ID:	17383Click image for larger version.
ID:	17384Click image for larger version.
ID:	17385Click image for larger version.
  2. #12
    Join Date
    Apr 2017
    Florida
    Posts
    45
    Quote Originally Posted by mwm1752 View Post
    Who are "they"? & which code cycle are they expecting the panel to be compliant with? If "they" are a home inspection service that would explain alot
    Yes, its a home inspection service. It's an abandoned house and I have no access to the report. They stated the issues with the panel needed to be addressed and I'm not seeing it. I'm beginning to doubt my own abilities.
  3. #13
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,985
    seeing the CU & undersized neutral it appears the feed into the panel is a piping system -- that said/assumed is there a disconnect ahead of this panel on the structure & would this be considered a feeder? All indications otherwise points to this being the service lateral which appears compliant.
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  4. #14
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,985
    Quote Originally Posted by Cybatrex View Post
    t
    They most likely are expecting the most recent code to apply the report should be accessible for proper repairs -- If so AFCI/GFCI is just the start of things they want improved even though there would be no code violations as is -- have they asked you to replace devices?
  5. #15
    Join Date
    Apr 2017
    Florida
    Posts
    45
    The only thing I found related to the system is this ripped off disconnect in the back yard which obviosly needs to be redone and this was obvious though.
ID:	17387Click image for larger version.
ID:	17388Click image for larger version.
  6. #16
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,695
    Different AHJ's have different allowances on how far service conductors are allowed to enter a building before they must hit the service disconnecting means. If that were a building on a slab and less then 5 feet before hitting the panel - it would be ok here.
    Looks maybe like for an air conditioner/heat pump that is no longer there, may have been taken out because the unit was removed and this would prevent energizing the exposed conductors?
  7. #17
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,706
    Quote Originally Posted by electrofelon View Post
    Only thing I see is the white conductors used as ungrounded conductors are not identified. I see the green screw so ok to have N and G together (some people like to keep them separate anyway, for appearance).
    Are those two breaker positions being used for whole house surge suppression?
  8. #18
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Am I the only one who is seeing a bare #6/#4 ground wire on the bottom lug that doesnt go to squat? It just appears to die at the bottom of the panel.
  9. #19
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,600
    Quote Originally Posted by JFletcher View Post
    Yes, you are.
    There is usually a small hole in that area for the GEC. At least there is on the panels I use.
    Tom
    TBLO
  10. #20
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by ptonsparky View Post
    Yes, you are.
    I saw it once I blew up the photo. I need glasses, or maybe a better monitor.
    eta: I retract my "self grounding panel" remark as well. ty for the correction.