    communication pul box

    In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes?

  2. #2
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,171
    Quote Originally Posted by jjavier View Post
    In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes?
    That rule is specific to #4 and larger conductors. I don't think you'll have a communication cable that large. In any case, you still do need to plan for proper bend radius.