Thread: PVC use indoors

  1. #11
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,047
    Quote Originally Posted by raberding View Post
    probably not allowed in plenums
    The meaning of the word plenum is a little confusing.

    To clarify, no wiring that is not directly necessary for the functionality of the air handling system is allowed in physically constructed ducts or plenums. Examples of such wiring are air temperature/speed sensor wiring or fan power/control wiring, that has no other option other than to be in the physically constructed duct/plenum. To contrast with physically constructed plenums, a plenum space, built with building walls and ceilings instead of duct walls, is where you either need a metal wiring method, or plenum-rated cable.

  2. #12
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    1,867
    Quote Originally Posted by A/A Fuel GTX View Post
    A good percentage of them are for venting and have no liquid in them.

    j
    Just methane gas
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  3. #13
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,131
    Quote Originally Posted by Carultch View Post
    The meaning of the word plenum is a little confusing.

    To clarify, no wiring that is not directly necessary for the functionality of the air handling system is allowed in physically constructed ducts or plenums. Examples of such wiring are air temperature/speed sensor wiring or fan power/control wiring, that has no other option other than to be in the physically constructed duct/plenum. To contrast with physically constructed plenums, a plenum space, built with building walls and ceilings instead of duct walls, is where you either need a metal wiring method, or plenum-rated cable.
    I think 300.22(B) & (C) makes it clear that PVC is not permitted in ducts and other spaces used for environmental air (plenums).

    I was trying to see about inside walls, etc.
    Ron

  4. #14
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    16,874
    Quote Originally Posted by ron View Post
    I think 300.22(B) & (C) makes it clear that PVC is not permitted in ducts and other spaces used for environmental air (plenums).

    I was trying to see about inside walls, etc.
    I think that the determining characteristic would not be residential versus commercial, but rather the building construction type required for the specific building occupancy.

  5. #15
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,131
    Quote Originally Posted by GoldDigger View Post
    I think that the determining characteristic would not be residential versus commercial, but rather the building construction type required for the specific building occupancy.
    I know that exists for NM cable, but couldn't find that for PVC
    Ron

  6. #16
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    16,874
    I don't think it is there.
    There may be contract terms requiring a metallic raceway or cable though.

    Sent from my XT1585 using Tapatalk

  7. #17
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,356
    I dont see a reason why RPVC couldnt be used indoors. Ive run many a thousand of feet of ENT for comm cable, tho it's not permitted in an air handling space (300.22?).
    Electricians do it until it Hertz!

  8. #18
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,454
    IMO PVC conduit inside, exposed (above a suspended ceiling) just looks sloppy, and too much like a DIY job. 3/4" PVC has to be supported every 3 feet, 1 foot from a box. EMT is faster to install, and not EGC is required.
    Typically you'll see MC cable or a mix of MC and emt
    Moderator-Washington State
    Ancora Imparo

  9. #19
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,131
    Quote Originally Posted by GoldDigger View Post
    I don't think it is there.
    There may be contract terms requiring a metallic raceway or cable though.

    Sent from my XT1585 using Tapatalk
    Luckily I write the Contract terms. 😀
    Ron

  10. #20
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    30,808
    Quote Originally Posted by tom baker View Post
    IMO PVC conduit inside, exposed (above a suspended ceiling) just looks sloppy, and too much like a DIY job. 3/4" PVC has to be supported every 3 feet, 1 foot from a box. EMT is faster to install, and not EGC is required.
    Typically you'll see MC cable or a mix of MC and emt
    3/4 PVC can be up to 3 feet from box to first support as a general rule, and every 3 feet afterward.