kwired

Electron manager
Location
NE Nebraska
Does a disconnect for an animal clinic x ray room require the 30" wide by 3 ft out clearance as a subpanel?
This is something that can vary in interpretation of the rule. Generally that interpretation will be based on wording in 110.26(A) that says "likely to require examination, adjustment, servicing, or maintenance while energized".

Many places accept the fact that if there are overcurrent devices that it is more likely to apply to this rule. But if you have really strict interpretation you would need same clearances for most every component of the electrical system.
 