Results 1 to 8 of 8
Thread: Electrical Riser Rooms
  1. #1
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,984
    Trying to find code on thru floor requirements for fire rating around either the cables or duct banks?
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  2. #2
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,457
    300.21
    Ron
  3. #3
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,984
    Quote Originally Posted by ron View Post
    300.21
    Agree
    circumstances have all electrical riser rooms stacked directly above each other --- all walls have appropriate fire ratings from floor deck to ceiling deck (typically concrete over steel decking) -- are penetrations thru floor/ceiling decks considered to be penetrating a fire rated assembly?
  4. #4
    Join Date
    Dec 2010
    Posts
    1,378
    Quote Originally Posted by mwm1752 View Post
    Agree
    Yes, if the floor/ceiling decks are indeed fire rated assemblies, which is virtually certain.
    The more they overthink the plumbing, the easier it is to stop up the drain
  5. #5
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,984
    What is by definition with walls rated as such would create a shaft -- A shaft could have any type of floor/ceiling platform (corregated steel) that would not be rated so why would the choice of using a concrete decking type floor/ceiling have to be rated?
  6. #6
    Join Date
    Dec 2010
    Posts
    1,378
    If it has a floor, it is a room, not a shaft. Grating is not a floor.
    Attached Images Attached Images
  7. #7
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,984
    we are talking fire protection being in place on all sides and a hole through a floor would be an opening in successive floors -- why would a grated surface not be a floor? I think we agree if the assembly is rated it should be addressed is as far as the NEC goes -- the interpretation of the assemblies(floor/ceiling ) fire rating or not is a building issue.
  8. #8
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,984
    2 pics tell different tales
    Attached Thumbnails Attached Thumbnails Click image for larger version.
ID:	17392   Click image for larger version.