Thread: Crawl space lighting

  1. #1
    Join Date
    Feb 2005
    Location
    New England
    Posts
    1,053

    Crawl space lighting

    Is there a code proposal that would require open lighting in a crawlspace to be physically protected.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	download (1).jpg 
Views:	89 
Size:	4.3 KB 
ID:	17468   Click image for larger version. 

Name:	281753004467b6949b536a43ca9ae2c6.jpg 
Views:	77 
Size:	18.1 KB 
ID:	17469  

  2. #2
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,540
    No but due to someone breaking a lamp and a shock or electrocution?, crawl space lighting is now required to be GFCI protected.
    You can certainly put in a proposal, but due to the above I doubt it was pass.
    Moderator-Washington State
    Ancora Imparo

  3. #3
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,661
    They probably should be; I've smacked and broken more than one myself.

    If you can find accident reports involving crawlspace lighting, or carefully word a proposal, you may be able to get protection on crawlspace lights. Shock and electrocution are not the dangers that having sharp, hot, broken glass in your face/head are imo. I dont think it a bad idea but then again, here, crawlspace lights are an afterthought and done as cheaply as possible. There's usually one at the entrance and one near an HVAC unit, if it's lit at all.
    Electricians do it until it Hertz!