Thread: 200 amp services all electric houses

  1. #21
    Join Date
    Jul 2013
    Location
    Renton, WA
    Posts
    625
    Quote Originally Posted by Greg1707 View Post
    other was undersized?
    Couple points of reference:

    Own house, 5300 sq feet, 200A service.
    Have not tripped the 200A in 45 years (QO breakers). Have had a 48A electric pressure washer in use, 2 clothes dryers (about 25 A each), 25 A electric water heater, a 25A oven, and 5T heat pump (40A) all running at same time. Still under 200 A. Could maybe have one of the grandkids over using the pressure washer and start using the 280A stick welder? - maybe exceed 200 A then If all the lights turned on also?

    OTOH, son has an 800 sq ft studio with 200 A service, 200A panel was cheaper than a 100 A panel, plus poco won't hook up anything under 200A meter base. e.g.
    You may install a service panel or meter base/socket that is sized less than 200 A, but the service line and meter that PSE installs will be sized as if you were installing a 200 A service. If you are installing an underground service that is less than 200 A, your meter base/socket must meet the dimensional requirements for a 200 A underground meter base/socket,..........

    OTOH2. POCO installed just a 25 kVA transformer for 5 habitat townhouse units I worked on 6 years ago (gas heat and WH, but electric stove). Each unit had 200 A panel. Our habitat engineer asked them to put in a 50 kVA transformer, but Poco would not put in anything larger than 25 kVA until the 25 kVA ever failed or excess complaints of brownouts. AFAIK, the 25 kVA is still in place.




  2. #22
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,170
    As of January the minimum service buss bar I believe in CA needs to be 200A. Due to the future installation of Solar. Does not make sense to me. You still need to reduce the main if you want more than 40 a solar, or use a panel that is made for line side tap.

  3. #23
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,146
    Quote Originally Posted by Fulthrotl View Post
    SCE did the same gold medallion rollout in the 60's here.

    my house is one of them. someone changed out the gold medallion
    doorbell for a funky one... i'm looking for an original one to replace it.

    SCG sued SCE, and won, as the gold medallion program here *prohibited*
    gas service from being available on the property. in the late 60's, they added
    gas to the entire tract, and SCE paid for the retrofit. restraint of trade was a
    compelling argument, and edison lost.

    my parent's house in 1962 was gold medallion, and had an electric pool heater.
    and a 400 amp service. the first month we turned on the pool heater, the
    electric bill was larger than the mortgage payment. we never did that again.
    i was only 7, but remember standing in front of the electric panel, listening
    to the sound of the meter spinning when the pool heater was on.

    you could actually hear it whirring in there.

    https://www.thespruce.com/gold-medal...nition-1821516
    Consumers did the 'Medallion Home' thing back then, too. By the mid to late 70's, many people had electric bills higher than their house payments.
    Cheers and Stay Safe,

    Marky the Sparky

  4. #24
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,565
    Quote Originally Posted by K8MHZ View Post
    Consumers did the 'Medallion Home' thing back then, too. By the mid to late 70's, many people had electric bills higher than their house payments.
    When motor fuels were $4.00 a gallon or more some people spent more on a fuel refill then their vehicle was worth

  5. #25
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,146
    Quote Originally Posted by kwired View Post
    When motor fuels were $4.00 a gallon or more some people spent more on a fuel refill then their vehicle was worth
    And look what that got them. "Medallion" cars that are all electric.
    Cheers and Stay Safe,

    Marky the Sparky

  6. #26
    Join Date
    May 2011
    Posts
    3,655
    Quote Originally Posted by Sierrasparky View Post
    As of January the minimum service buss bar I believe in CA needs to be 200A. Due to the future installation of Solar. Does not make sense to me. You still need to reduce the main if you want more than 40 a solar, or use a panel that is made for line side tap.
    There are now 'solar ready' main panels that have a 225A busbar and thus allow 70A backfeed. That's what they really want. I haven't heard of the 200A requirement, there are also 'solar ready' panels at 100/125A.

    And this must be just for new construction, of course.

  7. #27
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,565
    Quote Originally Posted by jaggedben View Post
    There are now 'solar ready' main panels that have a 225A busbar and thus allow 70A backfeed. That's what they really want. I haven't heard of the 200A requirement, there are also 'solar ready' panels at 100/125A.

    And this must be just for new construction, of course.
    Seems logical it would be for all new services whether new construction or not.

  8. #28
    Join Date
    May 2011
    Posts
    3,655
    Quote Originally Posted by kwired View Post
    Seems logical it would be for all new services whether new construction or not.
    Well, the Venn diagram portion of new services that aren't new construction is very small. My point was that for existing services getting equipment upgraded, either this doesn't apply or it's not being widely enforced.

  9. #29
    Join Date
    May 2010
    Location
    Inside the Beltway
    Posts
    580
    BTW, that 800 Ampere Miami mansion I mentioned had six HVAC compressors in a row, back by the ATS for the generator.
    Oh, and multiple many-KW "instant on" point of use water heaters. And the sauna.

    Take THAT, Reddy Kilowatt....

  10. #30
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,025
    Quote Originally Posted by Open Neutral View Post
    BTW, that 800 Ampere Miami mansion I mentioned had six HVAC compressors in a row, back by the ATS for the generator.
    Oh, and multiple many-KW "instant on" point of use water heaters. And the sauna.

    Take THAT, Reddy Kilowatt....
    The better question is what size transformer did the poco use on that service?