Page 2 of 2 FirstFirst 12
Results 11 to 17 of 17
Thread: Shielded ground wire.
  1. #11
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by Inyoinspector View Post
    ... We also do 2 rods no closer than 6' apart so there is more than 8' in contact in the ground. ...
    NEC requires 8' in contact with earth for each rod electrode.
    I will have achieved my life's goal if I die with a smile on my face.
  2. #12
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,695
    Thanks to everyone for the replies. The armor is aluminum and is required here for any stranded ground. We also do 2 rods no closer than 6' apart so there is more than 8' in contact in the ground. No armor is required if its #6 or larger and solid, #8 solid would also need to mechanically protected. (At least according to the building official) Ca has a few extra codes.
    How often are you seeing smaller then 6 AWG GEC's?
    Though I could get by with 8 AWG in some instances, 6 AWG is smallest bare conductor I ever stock. Seems it would be less cost and hassle to just run 6 AWG then to sleeve 8 AWG with aluminum armor anyway.
    NEC never mentions any solid vs stranded difference from physical protection perspective.
    I also agree if the armor were steel it would need to be bonded to the contained conductor at both ends, aluminum should only need bonded in one place.
  3. #13
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    The armored grounding conductor pictured is a "ANTI-THEFT GROUND WIRE IN CONDUIT" model with steel armor crimped every 6" to 8". I would think no special bonding would be required.
  4. #14
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,775
    Quote Originally Posted by ActionDave View Post
    I would called that armored. I'd also say that is something I've never seen before, but I think there was a previous discussion about that stuff. 250.64 (E) is the code section that applies.
    You might be referring to this thread?
    Another Al in Minnesota
  5. #15
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,523
    Quote Originally Posted by al hildenbrand View Post
    That's it!
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  6. #16
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,775
    We have some controversy in regards to the need to bond the shielding at the ground clamp to rod connection. When running two ground rods with shielded grounding wire do you need 2 clamps at the first rod in order to continue the bonding of the shielding material between the two rods or is the contact of the shielding to the wire sufficiently bonded?
    The pictured ground rod clamp / armored ground wire clamp (the MVP99) that you have in your earlier post, above, has these instructions:
    Click for Pg 1
    Click for Pg 2
    The web page for the MVP99 is available by clicking here.
    Note that the armor does NOT have to be removed for this specific clamp, per its instructions.
    If I were installing armored ground wire with this clamp, I would only use one clamp, unless I deliberately ended the wire, and attached a second length wire. That is, I wouldn't strip away any armor, and I'd follow the directions of the manufacturer and only install one clamp.
  7. #17
    Join Date
    May 2017
    Bishop, Ca USA
    Posts
    5
    Once again thanks to all for the clarification.
Posting Permissions
  • You may not post replies
  • You may not edit your posts