    type cable to car charger

    What type of cable do you recommend between the commercial building (2º floor) and the electric car charger (outdoor, underground pvc conduit)?

    We understand that UL fire requirements would be required, we are thinking in type TC cables.

  2. #2
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,066
    Bump
    If you aim at nothing, you will hit it every time!

  3. #3
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,324
    If you insist on staying with cable from the second floor all the way to the underground section uninterrupted then TC is about the only choice. MC and transition to THWN or conduit the whole way would be more typical for my area.